    A Nice Upgrade

    Homeowner had comfort issues. Typical 18 year old new construction home. Ductwork way undersized everything 6” runs unbalanced, the list goes on. Installed two stage furnace and two stage AC. Increase second floor runs to 7”, sealed ductwork and balanced. Happy customer.



    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter



    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    12,163
    Post Likes
    Beautiful work as always. Love that coil access door nice and open for service with nothing blocking it.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  4. Likes johoff34 liked this post.
  5. #4
    Join Date
    Jan 2014
    Location
    New England
    Posts
    7,539
    Post Likes
    You even kept it in the UTC family, my many relatives thanks you as they own UTX stocks and work for that corporations many divisions. So again thank you.

    Oh yea,.. BTW your installs always look great!

  6. Likes johoff34 liked this post.
  7. #5
    Join Date
    Jan 2019
    Location
    Vero Beach, Florida
    Posts
    794
    Post Likes
    Beautiful install. Sheet metal fab is such an amazing art. I wish i knew had to do it. Living in south Florida I don’t get a chance to do it.

    Excuse my ignorance; what’s that thing on the return plenum?

  8. Likes johoff34 liked this post.
  9. #6
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter
    Quote Originally Posted by Deathpunch0311 View Post
    Beautiful install. Sheet metal fab is such an amazing art. I wish i knew had to do it. Living in south Florida I don’t get a chance to do it.

    Excuse my ignorance; what’s that thing on the return plenum?
    No worries. I’m guessing you’re talking about the humidifier? Something I don’t imagine needing in Florida lol.


    Sent from my iPhone using Tapatalk

  10. #7
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter
    Quote Originally Posted by Bazooka Joey View Post
    You even kept it in the UTC family, my many relatives thanks you as they own UTX stocks and work for that corporations many divisions. So again thank you.

    Oh yea,.. BTW your installs always look great!
    You’re welcome. That’s pretty cool! I used to work for a Carrier dealer in the field. Now I work for a Carrier distributor doing field support and training.


    Sent from my iPhone using Tapatalk

  11. #8
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,316
    Post Likes
    It Seriously Looks Good Johoff.

    Is there a hanger on that gas line, so as to take the weight off of the gas valve?

    Is the outlet of the air cleaner blocked off somewhat?

    And, is that drain for the humidifier laying flat on the floor?
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  12. #9
    Join Date
    Jan 2019
    Location
    Vero Beach, Florida
    Posts
    794
    Post Likes
    Quote Originally Posted by johoff34 View Post
    No worries. I’m guessing you’re talking about the humidifier? Something I don’t imagine needing in Florida lol.


    Sent from my iPhone using Tapatalk
    Yep you’re right something not needed in Florida.

  13. #10
    Join Date
    Dec 2018
    Location
    Phoenix, AZ
    Posts
    343
    Post Likes
    The collar between the furnace and the evap coil casing is great. Makes for good measurements.

    Sent from my LG-M327 using Tapatalk

  14. Likes johoff34 liked this post.
  15. #11
    Join Date
    Jan 2014
    Location
    New England
    Posts
    7,539
    Post Likes
    Quote Originally Posted by johoff34 View Post
    You’re welcome. That’s pretty cool! I used to work for a Carrier dealer in the field. Now I work for a Carrier distributor doing field support and training.


    Sent from my iPhone using Tapatalk
    UTC is Headquartered in my state and the largest employer. In UTC umbrella Pratt & Whitney Aircraft engines being the largest employer. People tend to think ( especially here IMO ) that for the most part their HVAC brands and Automated Logic controls are their only lines. That's so far from the truth, until couple/three years ago they owned Sikorsky Helicopters, which is still based in my state, they own one of the world leader, Otis elevators, amount many other global reaching companies. Myself, thou I put Goodman Heat Pumps in my residence 15 years ago, and they are still going strong, no leaks, all original parts except the defrost boards.

  16. #12
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter
    Quote Originally Posted by DavidDeBord View Post
    It Seriously Looks Good Johoff.

    Is there a hanger on that gas line, so as to take the weight off of the gas valve?

    Is the outlet of the air cleaner blocked off somewhat?

    And, is that drain for the humidifier laying flat on the floor?
    Thank you.

    No hanger, main line is supported. I could of put a hanger there but missed it.

    The 6” box under the furnace is cut out for the air cleaner. Allows for all 20” to be used.

    No it’s sloped back.


    Sent from my iPhone using Tapatalk

  17. #13
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,316
    Post Likes
    Quote Originally Posted by johoff34 View Post
    Thank you.

    No hanger, main line is supported. I could of put a hanger there but missed it.

    The 6” box under the furnace is cut out for the air cleaner. Allows for all 20” to be used.

    No it’s sloped back.


    Sent from my iPhone using Tapatalk


    Again Sir, .... It's Looking Seriously Good!
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  18. #14
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    41,361
    Post Likes
    Hate to see the Mexican A/C but amazing work. Static is perfect, you don't see that much. The box under the furnace so the entire media cleaner gets airflow is rare. Keep showing us jobs like this. Might inspire better work from the rest of us!

  19. Likes johoff34 liked this post.
  20. #15
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    3,214
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    Hate to see the Mexican A/C but amazing work. Static is perfect, you don't see that much. The box under the furnace so the entire media cleaner gets airflow is rare. Keep showing us jobs like this. Might inspire better work from the rest of us!
    Its funny. You dont see static within specs very often but I have to say, the new company I am working for does a fine job on duct design. Most systems are .5-.6 tesp. Unheard of in the Portland area for new construction.

  21. #16
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter
    Quote Originally Posted by Adlerberts-Protege View Post
    Its funny. You dont see static within specs very often but I have to say, the new company I am working for does a fine job on duct design. Most systems are .5-.6 tesp. Unheard of in the Portland area for new construction.
    I feel like it’s easier for AOR to obtain it. I was in a meeting with a new dealer we were trying to convert from Trane. All new construction, they explained there systems on average are .9”-1.4” of static. I was thinking to myself please don’t get these people lol. More phone calls for me.


    Sent from my iPhone using Tapatalk

  22. #17
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    That is a beautiful install. Ever considered a little metal or clear plastic folder with the service/install manuals mounted on the system with a full start up report including static pressures, amps (with doors on) ect?

    We dont get installs like that around here and you cant blame anybody. The main concern is where is the bucket to puke in after spending half a day up in a sweltering muggy attic.

    Upside is static pressures aren’t usually much of a problem unless the system has been “upgraded” more then once or some odd design. Its easy enough to run big enough flex. Not so with basement units conditioning two story homes.


    Sent from my iPhone using Tapatalk

  23. #18
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Never mind... I now see your folder. Does that have a start up sheet in it? Tesp and drop across the coil would be awesome. Even better flue temp and other combustion numbers.


    Sent from my iPhone using Tapatalk

  24. #19
    Join Date
    Apr 2004
    Location
    Red Wing, MN
    Posts
    2,086
    Post Likes
    I see holes on either side of the air filter on the old unit. Did you by chance take TESP readings before you did the change out? How much of the duct did you modify? Looks fantastic!
    A Veteran is a person, who at some point in their life, wrote a blank check payable to the United States of America for payment up to and including their life.
    Gene Castagnetti-Director of the National Memorial Cemetery of the Pacific in Hawaii

  25. #20
    Join Date
    Mar 2014
    Location
    Grand Blanc
    Posts
    570
    Post Likes
    Thread Starter
    Quote Originally Posted by Core_d View Post
    Never mind... I now see your folder. Does that have a start up sheet in it? Tesp and drop across the coil would be awesome. Even better flue temp and other combustion numbers.


    Sent from my iPhone using Tapatalk
    Thanks. Yes I keep a commission sheet in there. I just use the Carrier ones, they’re pretty thorough.


    Sent from my iPhone using Tapatalk