    I have a couple of water cooled chillers running for about 6 years now, I have never been involved in the operation or maintenance of them until recently, and have noticed that the condenser approach is actually a negative figure. I dug out the commissioning documents from when the factory engineer started them on site, and they have been running a negative approach from day 1 it seems.

    Over the 3 chillers the approach varies from -2.3 to -6.2 degrees C. In my mind this is an extremely efficient condenser. But how is it possible for the approach to be negative? How is it that the liquid refrigerant is cooler than the condenser leaving water. And is it normal or acceptable for this to be happening.

    As some additional information, these chillers are running single 245 ton offloading screw compressors, and they have a desuperheater factory installed providing preheated water to potable water heat exchangers.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    27,232
    Post Likes
    How can you have negative #’s
    The refrigerant would be cooler the the condenser water.

    Not Possible!

  3. #3
    Join Date
    May 2019
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    How can you have negative #’s
    The refrigerant would be cooler the the condenser water.

    Not Possible!
    Well that's why I'm asking, because that is what is happening. The liquid line exiting the condenser is cooler that the water exiting the condenser. I took the readings multiple times to be sure using 3 different probes. Liquid line temperature readings were taken in the sensor well with the controller refrigerant temperature sensor.

    Cond. No. 1: Liquid Line=32.2 C Cond. Leaving Water=40.4 C Approach= -8.2 C
    Cond. No. 2: Liquid Line=33.3 C Cond. Leaving Water=39.2 C Approach= -5.9 C
    Cond. No. 3: Liquid Line=32.2 C Cond. Leaving Water=37.5 C Approach= -5.3 C

  4. #4
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,178
    Post Likes
    Quote Originally Posted by kris84 View Post
    Well that's why I'm asking, because that is what is happening. The liquid line exiting the condenser is cooler that the water exiting the condenser. I took the readings multiple times to be sure using 3 different probes. Liquid line temperature readings were taken in the sensor well with the controller refrigerant temperature sensor.

    Cond. No. 1: Liquid Line=32.2 C Cond. Leaving Water=40.4 C Approach= -8.2 C
    Cond. No. 2: Liquid Line=33.3 C Cond. Leaving Water=39.2 C Approach= -5.9 C
    Cond. No. 3: Liquid Line=32.2 C Cond. Leaving Water=37.5 C Approach= -5.3 C
    If I am reading this correctly, you used three different probes to recheck the leaving water temp.. However, the liquid temp. was from the controller refrigerant temperature sensor which is part of the original equipment and would have given the readings for the commissioning.

    Was a calibration of the controller refrigerant temperature sensor possibly required during the original installation?
    It's an upside down world we live in.

  5. #5
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,178
    Post Likes
    Another possibility.

    All three units were built custom at the same time. They were supposed to have 3K thermistors for the controller refrigerant temperature sensors, but 2.2K thermistors were installed in error. This would give refrigerant temperature readings below what they actually are.
    It's an upside down world we live in.

  6. #6
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,178
    Post Likes
    Quote Originally Posted by David Goodman View Post
    Another possibility.

    All three units were built custom at the same time. If They were supposed to have 3K thermistors for the controller refrigerant temperature sensors, but 2.2K thermistors were installed in error. This would give refrigerant temperature readings below what they actually are.
    There should have been an “if” included.
    It's an upside down world we live in.

  7. #7
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,091
    Post Likes
    Just curious, what is your entering condenser water temp?
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  8. #8
    Join Date
    Sep 2002
    Posts
    27,388
    Post Likes
    More efficient than the basics laws of physics - now That is some damned fine efficiency! <g> You would think those HX makers would want to patent their construction method !

    Joking aside: it seems that you have a measurement / sensing disparity. It is not possible to have even a 100% efficient heat exchange process. And yours is 100+% ? <g>

    You have a sensing issue in there somewhere - now you have to find it. Are all your readings taken independently? Or are you relying on the unit's control panel readouts?

    PHM
    ----------


    Quote Originally Posted by kris84 View Post
    I have a couple of water cooled chillers running for about 6 years now, I have never been involved in the operation or maintenance of them until recently, and have noticed that the condenser approach is actually a negative figure. I dug out the commissioning documents from when the factory engineer started them on site, and they have been running a negative approach from day 1 it seems.

    Over the 3 chillers the approach varies from -2.3 to -6.2 degrees C. In my mind this is an extremely efficient condenser. But how is it possible for the approach to be negative? How is it that the liquid refrigerant is cooler than the condenser leaving water. And is it normal or acceptable for this to be happening.

    As some additional information, these chillers are running single 245 ton offloading screw compressors, and they have a desuperheater factory installed providing preheated water to potable water heat exchangers.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,273
    Post Likes
    Do you have an economizer on the liquid line? The new Trane Agility mag bearing chiller has a plate frame heat exchanger on the liquid line where the liquid passes through one side of the heat exchanger on to the EXV feeding the evaporator and the other side of the heat exchanger is fed by another EXV which is fed with liquid teed off from the main liquid line and after going through the heat exchanger it’s vented to suction. This cools the liquid down below leaving water temp.

  10. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,178
    Post Likes
    If you have a restriction in the liquid line, and it acts as a metering device, you could have a colder temp than the water itself. But, I'm with Mikey on this. I think you have a sensor issue.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  11. #11
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,557
    Post Likes
    And yet again, a question where make, model, and serial number would help.