    Can someone tell me the output in inches water column these are designed for. Xv95 furnace. I want to get out of here today.

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Can someone tell me the output in inches water column these are designed for. Xv95 furnace. I want to get out of here today.
    The manuals Im looking at say 10.5"-11.0 wc.

    With that said, I like to use a combustion analyzer to set the proper manifold pressure in an attempt to get the unit between 6-9% O2.
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,264
    Post Likes
    Thread Starter
    Also, had a blower limit tripping due to the dumb insulators ripping my return flex off in the attic, flooding 100 degree air into it. What is a typical blower limit switch set at? Too lazy to look.

  4. #4
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Also, had a blower limit tripping due to the dumb insulators ripping my return flex off in the attic, flooding 100 degree air into it. What is a typical blower limit switch set at? Too lazy to look.
    If this is a TDH2 series, the "Reverse Flow Limit" on the blower housing OPENS at 105f, CLOSES at 95f.
    Instead of learning the tricks of the trade, learn the trade.

  5. #5
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,264
    Post Likes
    Thread Starter
    I dont know why it is called a reverse flow limit though. Not like the blower was drawing air back from the heat exchanger. It was just drawing hot air from the attic. Thanks for the specs though, its an xr95.

  6. #6
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Thanks for the specs though, its an xr95.
    Can you please post the full model number?
    Instead of learning the tricks of the trade, learn the trade.

  7. #7
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,264
    Post Likes
    Thread Starter
    Quote Originally Posted by rundawg View Post
    Can you please post the full model number?
    TDH1B065A9421CB

  8. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    TDH1B065A9421CB
    That is what I was afraid of. Some what of an odd ball unit.

    The LP kit for this unit states - 9.5"wc, and the Reverse Flow Switch has 95f/85f temps.

    Check your email.
    Instead of learning the tricks of the trade, learn the trade.

  9. #9
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,264
    Post Likes
    Thread Starter
    Quote Originally Posted by rundawg View Post
    That is what I was afraid of. Some what of an odd ball unit.

    The LP kit for this unit states - 9.5"wc, and the Reverse Flow Switch has 95f/85f temps.

    Check your email.
    Good. 9.5 is what i got. Cranked all the way down.

  10. #10
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    Good. 9.5 is what i got. Cranked all the way down.
    Any chance you put a combustion analyzer on it to see the results of that pressure setting?
    Instead of learning the tricks of the trade, learn the trade.

  11. #11
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,264
    Post Likes
    Thread Starter
    Quote Originally Posted by rundawg View Post
    That is what I was afraid of. Some what of an odd ball unit.

    The LP kit for this unit states - 9.5"wc, and the Reverse Flow Switch has 95f/85f temps.

    Check your email.
    What makes that a rare furnace? I guess trane's fix is a 6" spacer between furnace and coil and higher threshold limit switch to keep them from tripping. BS in my opinion.

  12. #12
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,870
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    What makes that a rare furnace?
    Most are set to 10.5"-11.0" wc for LP.
    Instead of learning the tricks of the trade, learn the trade.

  13. #13
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,614
    Post Likes
    Ive been away from resi, but back in the day, the AUH, AUY, AUX series used to be notoriously underfired with the 56 orifices in the LP kit.