    Micro channel coil care, on a unit with a compressor burnout

    Carrier - Model# 38AUZA07A0G5A0A0A0

    This unit has a micro channel condenser coil. I found the compressor windings are shorted to ground. I tested refrigerant acidity, with an instant test strip, which indicated it was acidic.
    My question/concern is.... If the aluminum micro channel coil, can't handle coil cleaning chemicals, how do they hold up with acidic refrigerant inside of it?
    Do I just do the RX-11 flush, replace the compressor, filter-dryer, vacuum to 500 microns, etc.
    ....or should I plan on replacing the coil as well...?

    I called Carrier, and they told me, "I'm not sure."

    Sent from my SM-G960U using Tapatalk

  2. #2
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Yep....you were talking to Carrier all right. I am not sure....is the standard answer.
    Quote Originally Posted by wreakingHaVAC View Post
    Carrier - Model# 38AUZA07A0G5A0A0A0

    This unit has a micro channel condenser coil. I found the compressor windings are shorted to ground. I tested refrigerant acidity, with an instant test strip, which indicated it was acidic.
    My question/concern is.... If the aluminum micro channel coil, can't handle coil cleaning chemicals, how do they hold up with acidic refrigerant inside of it?
    Do I just do the RX-11 flush, replace the compressor, filter-dryer, vacuum to 500 microns, etc.
    ....or should I plan on replacing the coil as well...?

    I called Carrier, and they told me, "I'm not sure."

    Sent from my SM-G960U using Tapatalk
    Sent from my SM-G965W using Tapatalk

  3. #3
    Join Date
    Aug 2014
    Location
    Alberta, Canada
    Posts
    191
    Post Likes
    I have always treated burn outs with a suction line filter dryer specifically made for burn outs. (ask your wholesaler). You can avoid any concerns you have with using a chemical scrubber this way.

    Sporlan has an excellent article about this here: http://blog.parker.com/use-of-suctio...-after-burnout

    Recheck your acid levels after operating the system for a few days/week and keeping an eye on your pressure drop across the suction dryer.

    Quote Originally Posted by wreakingHaVAC View Post
    Carrier - Model# 38AUZA07A0G5A0A0A0

    This unit has a micro channel condenser coil. I found the compressor windings are shorted to ground. I tested refrigerant acidity, with an instant test strip, which indicated it was acidic.
    My question/concern is.... If the aluminum micro channel coil, can't handle coil cleaning chemicals, how do they hold up with acidic refrigerant inside of it?
    Do I just do the RX-11 flush, replace the compressor, filter-dryer, vacuum to 500 microns, etc.
    ....or should I plan on replacing the coil as well...?

    I called Carrier, and they told me, "I'm not sure."

    Sent from my SM-G960U using Tapatalk

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Putting RX11 in the coil means most of it will fall to the bottom and not blow out with nitrogen. I wouldn't want to do that. I think the idea of the high capacity driers is going to be your best bet. Then change once or twice or whatever it takes. Cut them open when you remove, see what it looks like in there.

  5. #5
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    Putting RX11 in the coil means most of it will fall to the bottom and not blow out with nitrogen. I wouldn't want to do that. I think the idea of the high capacity driers is going to be your best bet. Then change once or twice or whatever it takes. Cut them open when you remove, see what it looks like in there.
    I planned on using high acid dryers... my concern and question, is regarding weather the acidic refrigerant will hurt the integrity of an all-aluminum coil.

    Sent from my SM-G960U using Tapatalk

  6. #6
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Well if you look up the material compatibility of aluminium vs. Inorganic acids such as hydrochloric acid and hydrofluoric acid it is rated as poor.

    Sent from my SM-G965W using Tapatalk

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,734
    Post Likes
    Standard Clean up procedures. if your that concerned Acid Away. Follow the instructions!

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Standard Clean up procedures. if your that concerned Acid Away. Follow the instructions!
    ...or...QwikShot Acid Flush. That way everything, both the acid and the treatment, get removed by the dryer. Replace the dryer after that and you are done.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  9. #9
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    Well if you look up the material compatibility of aluminium vs. Inorganic acids such as hydrochloric acid and hydrofluoric acid it is rated as poor.

    Sent from my SM-G965W using Tapatalk
    Agreed. Which is the reason for my concern.

    Sent from my SM-G960U using Tapatalk

  10. #10
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    I am aware of the normal procedures, in the event of a burnout. I have used RX-11 flush and acid away in the past. However, my concern is if the aluminum, microchannel condenser coil; will be effected by the acidic refrigerant, currently sitting in it now. As well as the acid cleaning process...whether or not it's okay to use, on this coil type.

    Also, thank you for your replies. I do appreciate you taking the time to respond.

    Sent from my SM-G960U using Tapatalk

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by wreakingHaVAC View Post
    Agreed. Which is the reason for my concern.

    Sent from my SM-G960U using Tapatalk

    It's a worthy concern. That's why I made the Qwik Shot Acid Flush suggestion.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #12
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    It's a worthy concern. That's why I made the Qwik Shot Acid Flush suggestion.
    You think it would be okay to use, on this coil? I'll give it a shot.
    Thank you.

    Sent from my SM-G960U using Tapatalk

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by wreakingHaVAC View Post
    You think it would be okay to use, on this coil? I'll give it a shot.
    Thank you.

    Sent from my SM-G960U using Tapatalk

    You can always call tech support at Mainstream Engineering. They make it.

    https://www.qwik.com/
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  14. #14
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    You can always call tech support at Mainstream Engineering. They make it.

    https://www.qwik.com/
    They make what? The coil?

    Sent from my SM-G960U using Tapatalk

  15. #15
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,180
    Post Likes
    I appreciate your concern, and I hadn’t thought about the possible acid corrosion problem in these coils until I read your post.

    Aluminum micro channel coils have been around for more than 10 years now.

    It seems as though no one here has been experiencing problems after burnouts with these coils. So, it wouldn’t appear to be an issue. (at least not yet)
    It's an upside down world we live in.

  16. #16
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by David Goodman View Post
    I appreciate your concern, and I hadn’t thought about the possible acid corrosion problem in these coils until I read your post.

    Aluminum micro channel coils have been around for more than 10 years now.

    It seems as though no one here has been experiencing problems after burnouts with these coils. So, it wouldn’t appear to be an issue. (at least not yet)
    Thank you for your reply.
    You make a great point. I just know, that all manufacturers of this coil, state, "Wash coil with water only." That's what started the alarm bells in my head about acidic refrigerant.

    Sent from my SM-G960U using Tapatalk

  17. #17
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by wreakingHaVAC View Post
    They make what? The coil?

    Sent from my SM-G960U using Tapatalk
    Sorry... that was a stupid question. That's obviously the website of the quick shot acid wash....
    I will reach out to them and ask them. If they say it shouldn't be a problem, then I will try it. Thanks again.

    Sent from my SM-G960U using Tapatalk

  18. #18
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,180
    Post Likes
    Quote Originally Posted by wreakingHaVAC View Post
    Thank you for your reply.
    You make a great point. I just know, that all manufacturers of this coil, state, "Wash coil with water only." That's what started the alarm bells in my head about acidic refrigerant.

    Sent from my SM-G960U using Tapatalk
    And water works so well on greasy restaurant package units.
    It's an upside down world we live in.

  19. #19
    Join Date
    Jul 2018
    Posts
    50
    Post Likes
    Thread Starter
    Quote Originally Posted by David Goodman View Post
    And water works so well on greasy restaurant package units.
    Ha!

    Sent from my SM-G960U using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •