    T&B on a loop.

    Another thread reminded me of an interesting problem/solution. It was a small AH 20000 cfm.
    The installed duct wouldn't deliver on the end terminals.
    The engineers asked to do several things but eventually told the tinner to create a loop. Branch the supply with a pair of pants and connect the two together at the end of the runs.
    Pressurize the duct in two directions.

    I can remember homes that had a perimeter loop. I think the practice went away because of the extra ducts required.
    This was the first time I had seen it used but it did solve the air problem. I'm not sure how to figure things like friction and predict cfm.
    Anyone ever run into this design today?
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  2. #2
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Ive never worked on one, but seen the design at a chipotle. I think mainly it was for looks in that case, as the duct was exposed.

    But near the ends of the runs, the only measurements that would be accurate would be from the grills.

    Maybe 75% way down the run, a traverse may prove dubious.

    Curious what Wayne thinks.




    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Mar 2005
    Posts
    1,762
    Post Likes
    most the trane intellipak vav systems I saw were ducted like this
    Keep it simple to keep it cool!

  4. #4
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The duct loop theoretically cuts the velocity in half and thus the friction losses. What actually happens depends on the load distribution and the load proximity to the origin of the air supply to the load. The main place I have seen this design is in gymnasiums. They work close to the design theory because the relative location of the diffusers and airflows are all the same. I haven't seen this design implemented on a VAV system. If this has to be used on a VAV system the diversity would probably be 25 to 30% or maybe more. What makes undersized ducts a problem on VAV'S is the air may be available to the VAV but at too low a pressure for the VAV to deliver airflow close to design. VAV'S and FPB'S should have at least 1/2 inch of static at the box inlet.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. #5
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Thread Starter
    I might think this system could save metal because the initial run would be smaller but more fo it. Smaller ducts overall are cheaper in metal and labor. The design in the post was to solve a problem but I also know it's a valid design.

    Off the plenum the runs would be smaller but could be staged like an equal friction or how it might be an advantage for static regain. I'm not familiar with the velocity reduction method. I also wonder if /how it might affect dynamic losses.
    I also wonder if this idea might be used for other poor designs that failed to deliver on end runs. If running another small duct to the end runs rather than demoing or modifying the whole duct system. Just pondering.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •