    How often are you pulling evaporator heads on your Centrifugals??? (York YK's here)

    Happy "Friday Eve" e'rrrbody!

    So, I've noticed lately at my current employer, we're falling further behind on our chiller annuals, and as a result being forced to run inefficient machines as these spring cooling loads pick up...

    Annuals here consist of pulling both condenser and evaporator heads, brushing all tubes, borescope inspection of a few on each side, etc. Both sides are typically spotless. We have very clean chilled water on the evaporator side, with an abundance of side-stream filtration and impeccable water treatment. All chillers are either York YK or OM Titans.

    At my previous employer, we had the same fantastic water treatment, York YK's, and only pulled evaporator heads to brush/scope tubes every 3-5 years, also finding them to be pristine... and this despite having no side-stream CHW filtration there.

    I'm thinking of suggesting we move to a similar strategy at my current employer, with the obvious benefit of getting through annuals more quickly, and I'm curious what some of you guys have experienced with your annuals...

    Thanks!
    Last edited by leander311; 04-18-2019 at 01:07 PM.

  2. #2
    Join Date
    Jan 2015
    Location
    Somewhere making cold water
    Posts
    370
    Post Likes
    Once every 3-5 years when we do eddy current test.

    Sent from my SM-G950U using Tapatalk

  3. #3
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    5-6 years depending on owners insurance underwriters, due eddy current at that time on both heat exchangers.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Jun 2008
    Location
    Ohio
    Posts
    34
    Post Likes
    Generally every five years

  5. #5
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Depends on how much money the customer wants to spend .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. Likes BALloyd liked this post.
  7. #6
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    341
    Post Likes
    Eddy Current is very important .

  8. #7
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Assuming it's a closed chilled water system, I would follow York's recommendation on eddy current frequency and only pull the evaporator heads then. Unless I suspected problems, of course.
    In honor of RichardL: "Ain't 'None' of us as smart as 'All' of us".

  9. #8
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    We recomment clean and eddy current on a 5 year cycle with good water qaulity.

    Question/comment. Your thought could be a two edged sword. If you are doing this for a customer your boss may not want to recommend this and give up that annual income. If this is for chillers your company owns there are no drawback just less maintenance cost. For the most part I base any extra cleaning recomendation on chiller performance, pressure, temps, amps, load changes, unexplained loss of refrigerant...... otherwise every 5 years

  10. #9
    Join Date
    Dec 2018
    Location
    Phoenix, AZ
    Posts
    788
    Post Likes
    Some people do ECT every 3 years for CDW and every 6 for CHW. Some do 2 and 4. Some do 3 and 5.

    Sent from my LG-M327 using Tapatalk

  11. #10
    Join Date
    Dec 2018
    Location
    Texas
    Posts
    29
    Post Likes
    Condenser, Brush tubes annually and eddy current every 2-3 years
    Evaporator, Brush tubes and eddy current every 5 years.
    Once heavy wear or a problem is identified, eddy current is recommended every year

  12. #11
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    381
    Post Likes
    Quote Originally Posted by ChillerTech3384 View Post
    Condenser, Brush tubes annually and eddy current every 2-3 years
    Evaporator, Brush tubes and eddy current every 5 years.
    Once heavy wear or a problem is identified, eddy current is recommended every year
    Very good advice here.

  13. #12
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    depends on water quality. we have 2 sites with horribly dirty chilled water loops...neither will spend the money on filtration. One site we had to brush the evaporator twice in a year, the other, we had to do last spring, and I'm going tomorrow to do it again.

    If you have good quality treatment and clean loops, what they said....

  14. #13
    Join Date
    May 2006
    Location
    Austin, TX
    Posts
    111
    Post Likes
    Thread Starter
    Thanks everyone. Very good insight. We're almost to that time of year again, so hopefully, with all your input, this will get some traction.

  15. #14
    Join Date
    Jun 2005
    Location
    SE PA
    Posts
    15
    Post Likes
    Every 3 years. Customers with multiple machines we only do 1/3 of the machines at a time. One of my jobs has 6 chillers so we do 2 each year.

  16. #15
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    201
    Post Likes
    You may need to confer with the boss, if the customers are paying for this every year. It is additional charge and there fore income for tour company.
    2nd: your customer Base will notice the lack of attention. Which could him to question the contract structure and cost.
    This can open the door for a competitor to walk in.

  17. #16
    Join Date
    Apr 2012
    Location
    So.Fl. & NYC
    Posts
    201
    Post Likes
    Hi guys, in our office in Miami, we would alternate removing heads during the annual inspections and tube brushing. Giving us an opportunity to install fresh gaskets and exercise all nuts and bolts. The evap was usually done on a 2-3 year basis in same manner. forgive the spell check errors above

  18. #17
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Last facility I was at had 4 Carriers. No ECT since install, 10 years. Did 1 every year each year until I left 3 years ago. Oil analyses on all every year!

    It's more about a base line and history to see problems Before they arise!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •