    Which brings up another point. So far, for whatever reason, I've been thinking air flow for the most part.

    When it comes to hydronics, then it can be much more critical. Sure, you might get lucky, but in my experience, balancing the flow through the various devices is very important for proper operation, long life, and overall efficiency.
    I do a triple evac with nitro to remove non condensables.

  2. #22
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Chilled water balance is the most critical. Hot water is so forgiving it's hard to screw up unless the system is under designed. Chilled water balance forces water where you want it by limiting the amount of water any device can take. If not balanced properly chilled water systems can be a disaster. Believe it or not most balancers are not good at water balance.
    No man can be both ignorant and free.
    Thomas Jefferson

  3. #23
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,458
    Post Likes
    I've done a few through the years. Depending on the age of the system, the location of the circuit setters, and if the original engineering prints are available, sometimes it goes fast, but it usually takes more time than you think it will. At least if you keep going back to check and recheck everything after you've already made one or two passes.


    Quote Originally Posted by WAYNE3298 View Post
    Chilled water balance is the most critical. Hot water is so forgiving it's hard to screw up unless the system is under designed. Chilled water balance forces water where you want it by limiting the amount of water any device can take. If not balanced properly chilled water systems can be a disaster. Believe it or not most balancers are not good at water balance.
    I do a triple evac with nitro to remove non condensables.

  4. #24
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    After you have done a lot of water balance it gets a lot easier. The recommended method is to preset the circuit setters by calculating the pressure drop needed. In my opinion that is a waste of time. If you start nearest the pump and set the flow slightly lower than design two passes will usually do it. When I was doing a lot of water balance I fairly often got almost all of them on the first pass. Even at that you still have to read the circuit setters twice.
    No man can be both ignorant and free.
    Thomas Jefferson

  5. #25
    Join Date
    Oct 2016
    Posts
    3,838
    Post Likes
    Wayne, we always use auto-flow valves on vavs. They still need to be checked during tab, but no adjustment needed.

  6. #26
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Wayne,
    To respond to the title of the thread, ABSOLUTELY in the context of Hydronics and VAV Systems !
    After being a "Controls Guy" for 23+ years a good TAB person is worth every cent.

    Readers Digest version of 1 particular project: 7 Story building retrofit of 2 RTU's and 150+ VAV boxes. Told the customer "you really need to re-balance". They drug their feet for 6 month, finally consented and we recommended 3 TAB companies (all 3 excellent). 6 months after TAB completed Chief Building Engineer tells me that the "Energy savings paid for the Balance 2 month ago" !

    I agree with retro-commissioning, to a point. Too many of the folks that do it try to justify their existence with a mountain of paperwork and less than complete TAB.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  7. #27
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Quote Originally Posted by Scoobie View Post
    Wayne, we always use auto-flow valves on vavs. They still need to be checked during tab, but no adjustment needed.
    With those, the more important part of the balancing is the riser balance in a high rise, or the main branch lines in a more sprawling system.

    The smaller terminals are less important, but the key to any balance is a completed system, clean strainers, correct rotation, and every valve open and a properly filled system .

    But most times balancing is “done” in steps before the system is totally complete.




    Sent from my iPhone using Tapatalk

  8. #28
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,458
    Post Likes
    Yeah, I'm sure if I did a lot more of it, I would've gotten faster/better. But since I only did a few, and probably a year or more apart, well, you get the idea.


    Quote Originally Posted by WAYNE3298 View Post
    After you have done a lot of water balance it gets a lot easier. The recommended method is to preset the circuit setters by calculating the pressure drop needed. In my opinion that is a waste of time. If you start nearest the pump and set the flow slightly lower than design two passes will usually do it. When I was doing a lot of water balance I fairly often got almost all of them on the first pass. Even at that you still have to read the circuit setters twice.
    I do a triple evac with nitro to remove non condensables.

  9. #29
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Scoobie,
    The auto flow valves do control maximum flow. Reading the pressure drop across them only tells you if you have enough differential across the valve for it to work but doesn't tell the flow. When I was balancing full time the complaint with them was they started having problems after about 2 years. I don't know if that's still true.
    No man can be both ignorant and free.
    Thomas Jefferson

  10. #30
    Join Date
    Oct 2016
    Posts
    3,838
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    Scoobie,
    The auto flow valves do control maximum flow. Reading the pressure drop across them only tells you if you have enough differential across the valve for it to work but doesn't tell the flow. When I was balancing full time the complaint with them was they started having problems after about 2 years. I don't know if that's still true.
    It’s the norm around here on big or small jobs. Tab guys ain’t real happy if you use circuit setters. Pressure independent control valves is the new hot thing. I personally don’t see what’s so great about the picv s.

  11. #31
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Heatingman the reason some engineers hated me is I did make them accountable. There were contractors that banned me from meetings because as they said "we are afraid of what you will say". I told them the truth and apparently it hurt. I had engineers trying to tell me how to test HVAC systems that had never done it even one time. One engineer who not only didn't know my job but didn't know his either said I was doing my own thing. I said you are damn right I am and it is my thing not yours. One thing I enjoyed was when the fire marshal came to witness testing of the smoke fans the engineer poised himself to supervise the test. The fire marshal ask who was the balancer and found out it was me. He turned to the engineer and said the balancer is going to run this test.
    No man can be both ignorant and free.
    Thomas Jefferson

  12. Likes heatingman liked this post.
  13. #32
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Thread Starter
    Why don't the TAB guys like circuit setters? Usually the ones I knew that didn't like them didn't like water balance because they didn't know how to do it. I don't like the circuit setters that read out in inches because it doesn't take much system instability to make them impossible to set.
    No man can be both ignorant and free.
    Thomas Jefferson

  14. #33
    Join Date
    Oct 2016
    Posts
    3,838
    Post Likes
    They know how to balance them. They just take a lot longer.

  15. #34
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,458
    Post Likes
    LOL


    Quote Originally Posted by WAYNE3298 View Post
    Heatingman the reason some engineers hated me is I did make them accountable. There were contractors that banned me from meetings because as they said "we are afraid of what you will say". I told them the truth and apparently it hurt. I had engineers trying to tell me how to test HVAC systems that had never done it even one time. One engineer who not only didn't know my job but didn't know his either said I was doing my own thing. I said you are damn right I am and it is my thing not yours. One thing I enjoyed was when the fire marshal came to witness testing of the smoke fans the engineer poised himself to supervise the test. The fire marshal ask who was the balancer and found out it was me. He turned to the engineer and said the balancer is going to run this test.
    I do a triple evac with nitro to remove non condensables.

  16. #35
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    I think he only reason T&B is done at all is it's on the spec. or complaints are through the roof.
    I remember reading a T&B report in a contractors office. I told them that the report was incorrect. He told me he didn't care. All he cared about was the NEBB stamp. Getting paid was most important.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •