    OK, I'm not going to just hand you the answer on this one.
    1. What's wrong with this picture?
    2. Why should it not be that way?
    3. Guess how it actually got installed on site.
Size:  49.4 KBName:  JustLegend.png
    Jun 2012
    Northern NV
    Pump on drain? Only thing that jumped out. Don't fool with too many towers.
    Seems odd that a bypass would dump in the pan tho.. Situation for an overflow IMHO
    Did I get something?
    May 2009
    SC
    Quote Originally Posted by Juan Madera View Post
    No drain pump needed, these are 10' above ground level and gravity drain seems to work fine.
    Bypass dumping in the pan is kinda nice, keeps things stirred up IMO.
    Mar 2016
    Pahrump, NV
    I’m commenting mostly to learn and follow this post. I don’t have any cooling towers.
    The 20” common supply and return lines would seem to be a bit small for three units with each having 12” return and supply. I’m thinking 22” commons would be a better match.
    Even though each unit has 14” equalizer lines, with only three units connected, the equalizer pipe between the units should be more like 10”.
    I’m not writing with any authority.
    It's an upside down world we live in.
    May 2009
    SC
    I honestly couldn't say anything about the pipe sizing, I hadn't thought about it on that level honestly. I'm not at the level where I check engineers math at that.
    This is more of a sequence of operation fail.
    kansas
    How big a pit do you have to bury these in for the Chwr to prime and work right
    Jun 2008
    Windsor, Ont.
    Balancing flow is my 1st concern. Secondly if the equalizing line is physically below the towers as shown I expect it will eventually become a huge pocket for debris to collect and difficult to clear or drain. I can only assume in SC you don’t have winter operation concerns like we do here with this equalizing line.
    Apr 2017
    The Deep South
    I agree with NYRB, the towers should have been piped reverse return to balance the flow. Other than that, I just have some minor observations at first glance, nothing glaring.
    May 2014
    Bay Area California
    Just one bypass? Couldn't that create service problems?
    I do a triple evac with nitro to remove non condensables.
    May 2014
    Bay Area California
    Or put the bypass on the main headers, not just one tower.
    Quote Originally Posted by BBeerme View Post
    May 2009
    SC
    OK, maybe more than one issue with this thing! I do know the final result balancing line was insulated and each pan has heat, I'm not worried about freezing in my climate and the hospital needs cooling 24/7/365 so these will be in use all winter long. Bryn, was that balance insulated or was there some disassembly before this picture was taken?
    The direction I was heading was let's say each tower is sized for a 800 ton chiller and your overall plant load is only 300 tons or less in the winter so you are only needing one tower and you do need the bypass valve to keep the CW temp from getting to low when OAT is in the 40°s.
    May 2009
    SC
    Quote Originally Posted by JCN View Post
    What do you mean reverse return? At the moment the CW circulation pumps move the water through the chillers and eventually the top of the towers.
    Feb 2016
    Louisburg Kansas
    The sketch shown is only a schematic so criticizing the actual install is not possible. I would have put a bypass on each tower for redundancy especially this being a hospital. Reverse return or not the tower distribution should be balanced.
    Thomas Jefferson