    Replaced Cond Fan, can't cool below 10deg now

    Half ton system. Walk-in freezer, low temp. Only replaceed the evaporator motor - old motor would barely spin.. Then all of a sudden the system can't get below 10 degrees. We never cracked the system, or lost refrigerant. Checked the expansion valve and condenser coils. They look good, and are Distributing evenly. System Cycles well if set to 20 degrees. So this is more of a theory question - why would only replacing the fan change any of the Dynamics?

  2. #2
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Are you a professional service technician or are you the equipment owner?
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Define "Looks Good" that must be one of the things I've forgotten how to do!

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes

  5. #5
    Join Date
    Apr 2019
    Posts
    4
    Post Likes
    Thread Starter
    Yeah that's pretty sloppy. What I mean by that is the frost is evenly distributed and doesn't indicate that I need to make any adjustments. I usually use that is a go no-go indicator what's the weather or not expansion valve needs to be tweaked.

  6. #6
    Join Date
    Apr 2019
    Posts
    4
    Post Likes
    Thread Starter
    Both

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    What's the SH at the Outlet?
    What's the SH at the pump?
    SG Clear?
    Amps?
    Head Master?
    Head Pressure
    Receiver?



    Frost just means below freezing!

  8. #8
    Join Date
    Apr 2019
    Posts
    4
    Post Likes
    Thread Starter
    I will check those tommrow and post, thx.

  9. #9
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    Shine a flashlight thru the evap coil to see if its frozen up. Defrost schedule may not be able to overcome a dead evap motor

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Quote Originally Posted by SonRise View Post
    I will check those tommrow and post, thx.
    Update after 2 weeks!

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    If you are a service tech, this is in the wrong area.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •