    2 years old new Trane chiller RTAC, now chiller tube have broken and water entered into the entire circuit. I was told by Trane office that the maintenance might be bad. But the maintenance contractor is not ready to take over any responsibility. Now eddy current test is in progress…but as in a client side what a cost imposed by this ….now there have feelings that trane now do not maintain their quality and reputation, what do you think
    Attached Thumbnails Attached Thumbnails EDDY TEST.jpg  

  2. #2
    Join Date
    Nov 2011
    Location
    GA
    Posts
    516
    Post Likes
    Does the chiller have control of the pump, flow proving working properly? What were the eddy current results, what caused the failure?

    Sent from my SM-G950U using Tapatalk
    Life's tough, it's even tougher if your stupid

  3. #3
    Join Date
    Feb 2017
    Location
    New York
    Posts
    1,528
    Post Likes
    Quote Originally Posted by GAchillrtek View Post
    Does the chiller have control of the pump, flow proving working properly? What were the eddy current results, what caused the failure?

    Sent from my SM-G950U using Tapatalk
    Yes, that is one thing that is overlooked by a lot of controls contractors. Whoever has the BMS, usually wants to control the pumps. The chillers should be controlling the pumps. What does it have for a flow switch and is it operational?
    -----Stop, step back, relax and have another go at it.-----

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,453
    Post Likes
    Also, any isolation valves on the chilled water should be controlled by the chiller. I heard of a bundle ruptured by freeze damage due to the isolation valves were controlled by building controls while the pump was controlled by the chiller.
    In honor of RichardL: "Ain't 'None' of us as smart as 'All' of us".

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,453
    Post Likes
    It sounds early in the "investigation" to be assigning blame for the failure, and accusations that nobody is standing behind their service and/or product.
    In honor of RichardL: "Ain't 'None' of us as smart as 'All' of us".

  6. Likes GAchillrtek liked this post
  7. #6
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,366
    Post Likes
    What is eddy current showing, tube wall thinning or rupture?

    How did the tube(s) fail, freeze or corrosion?

    This needs to be determined before any corrective actions can be taken and/or blame(responcability) assigned

  8. #7
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    543
    Post Likes
    Thread Starter
    the eddy current test still have not produced, I am waiting for that. i will update here. the flow switch does work well, it was tested in the presents of Trane tech.

  9. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,203
    Post Likes
    Quote Originally Posted by moideen View Post
    the eddy current test still have not produced, I am waiting for that. i will update here. the flow switch does work well, it was tested in the presents of Trane tech.
    Does the chiller control the pump?

  10. #9
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,132
    Post Likes
    Trane has to be involved pulling and accessing tube. Because there will be a lawsuit. Were talking a whole new machine. Don't be caught up with what if
    you might have to testifie or someone might overhear what you said.

  11. #10
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,249
    Post Likes
    Quote Originally Posted by servicefitter View Post
    Trane has to be involved pulling and accessing tube. Because there will be a lawsuit. Were talking a whole new machine. Don't be caught up with what if
    you might have to testifie or someone might overhear what you said.
    He is in the middle east, their legal system is way different than ours, there aren't any lawsuits there, if proven that Trane sold them a "lemon" chiller the salesman would be given two choices "death by public stoning or beheading".
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  12. #11
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    543
    Post Likes
    Thread Starter
    Quote Originally Posted by R123 View Post
    Does the chiller control the pump?
    the BMS is in defunct. so there is no interlock with chilled water pump. but the flow switch operation is healthy.there is 2 additional chillers on this same block. this accident open my eyes to install water pressure differential switch as well as interlock with pump on urgent base

  13. #12
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    543
    Post Likes
    Thread Starter
    Quote Originally Posted by servicefitter View Post
    Trane has to be involved pulling and accessing tube. Because there will be a lawsuit. Were talking a whole new machine. Don't be caught up with what if
    you might have to testifie or someone might overhear what you said.
    the eddy current test is carrying out by trane..it is in progress

  14. #13
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    543
    Post Likes
    Thread Starter
    Quote Originally Posted by Answer-Man View Post
    What is eddy current showing, tube wall thinning or rupture?

    How did the tube(s) fail, freeze or corrosion?

    This needs to be determined before any corrective actions can be taken and/or blame(responcability) assigned
    still it is in progress, next working day, i will get the result. i will update...