Results 1 to 9 of 9
  1. #1
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    301
    Post Likes

    So now I have a carrier network tool

    We need to integrate a 30hx chiller thru bacnet thru a open upc module.Looking at some older post I see there's a automapping feature that need to be disabled.And I manually enable the point I want


    Q1
    Basically how do we do that?

    Q2
    CCN did not came with rj14 cable is it a standard rj14 cable or a carrier home made with reversed wire?

  2. #2
    Join Date
    Apr 2014
    Location
    MN
    Posts
    435
    Post Likes
    I don't think you need to enable anything on the CCN side.
    You'll have to build an equipment file thru equipmentbuilder for the 30hx chiller and download it into the UPC card.
    The rj14 cable is a straight thru cable if I remember right.

  3. #3
    Join Date
    Apr 2014
    Location
    MN
    Posts
    435
    Post Likes
    Also FYI, equipmentbuilder has programs for the 30HXA and the 30HXC with MMB versions 2 and 3.

  4. #4
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    301
    Post Likes
    Thread Starter
    Open upc was factory installed.
    We want to do a integration from what I heard there is a automapping feature that grab 50 point.
    Is that right

  5. #5
    Join Date
    Dec 2005
    Location
    California
    Posts
    629
    Post Likes
    Quote Originally Posted by patpinet View Post
    Open upc was factory installed.
    We want to do a integration from what I heard there is a automapping feature that grab 50 point.
    Is that right
    The Open UPC card is already bacnet MS/TP. Just give it an address and discover your points.
    Controls, the cause of... and solution to... all your HVAC problems.

  6. #6
    Join Date
    Apr 2014
    Location
    MN
    Posts
    435
    Post Likes
    The auto mapping was the older translator card. Most everything you'll need is setup in the UPC card.

  7. #7
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    301
    Post Likes
    Thread Starter
    Quote Originally Posted by bacnet>CCN View Post
    The auto mapping was the older translator card. Most everything you'll need is setup in the UPC card.
    Thanks

  8. #8
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    311
    Post Likes
    did you get done what you needed?

  9. #9
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    301
    Post Likes
    Thread Starter
    Not yet this is only a small part of a bigger project.
    Should be done in May.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •