Thread: Carrier 30RBC AquaSnap alarm A2.01

  1. #1
    Join Date
    Mar 2008
    Location
    Mesa, Az
    Posts
    109
    Post Likes

    Carrier 30RBC AquaSnap alarm A2.01

    Carrier AquaSnap m#30RBC1206-BH40-L
    I’m getting a A2.01 alarm high motor temperature in compressor. Determined sensor is bad but compressor is still good. If this happens what do you guys usually do? Remove sensor and fake out on scroll protection module or replace with some type external sensor? Thanks for any insight guys

  2. #2
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    Is it a 25 ton Danfoss scroll? are you sure the sensor is bad or is the motor really getting hot? the 25 ton Danfoss scrolls have been shit as far as I'm concerned, I think I've read on here of other guys having problems as well. You can put a resistor across the sensor input on the SPM and see what happens, my money says it burns up.

  3. #3
    Join Date
    Mar 2008
    Location
    Mesa, Az
    Posts
    109
    Post Likes
    Thread Starter
    Quote Originally Posted by chillrdude View Post
    Is it a 25 ton Danfoss scroll? are you sure the sensor is bad or is the motor really getting hot? the 25 ton Danfoss scrolls have been shit as far as I'm concerned, I think I've read on here of other guys having problems as well. You can put a resistor across the sensor input on the SPM and see what happens, my money says it burns up.

    Circuit was locked out two compressor tandem circuit. Both ambient temperature. Cleared alarm and came right back. Resistance reading on sensor was above 4.5k ohms can’t remember exactly. Compressor ohms out good didn’t try starting circuit. Just wondering if anyone seen these internal PTC motor temp sensors fail. Would hate to replace whole compressor if just sensor is bad. Wondering what options I had and yes it is the blue danfoss compressor.

  4. #4
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    Do you have NSTV ? if so you could read the motor temps in real time, in the pics below Circuit A comp A was having a problem, at start up the ohm reading would be normal at 270ish within about 45 seconds of run time the motor temp sensor would be at 5k and shut off, customer wanted me to bypass the sensor, it burned up pretty quick.Click image for larger version. 

Name:	carrier1.jpg 
Views:	146 
Size:	84.9 KB 
ID:	807952Click image for larger version. 

Name:	oct18.jpg 
Views:	143 
Size:	112.4 KB 
ID:	807953

  5. #5
    Join Date
    Mar 2008
    Location
    Mesa, Az
    Posts
    109
    Post Likes
    Thread Starter
    Chillrdude,
    Appreciate the help. On your situation was compressor good and just sensor going out of range after some runtime? If so did you replace compressor or end up bypassing sensor of some sort? I’m heading back out Monday gonna bring a resistor and try to bypass and see if I can run compressor to verify comp and SPM are good.
    Attached Thumbnails Attached Thumbnails 416F974A-CEBF-44EC-9674-8E53E5FE8239.jpg  

  6. #6
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    The winding sensor was good and doing what it was supposed to, the motor was actually getting to hot, customer thought maybe the sensor was not working properly and wanted to try and bypass the sensor, it burnt up pretty quick as I recall. This particular chiller is a 210 ton unit with 3 circuits, circuits A & C are 3 25 ton Danfoss scrolls, circuit B is 3 20 ton Danfoss scrolls, it's a little over 5 years old and I've already replaced 5 or 6 of the 25 ton compressors, circuit B with the 20 ton scrolls has been great.

  7. #7
    Join Date
    Mar 2008
    Location
    Mesa, Az
    Posts
    109
    Post Likes
    Thread Starter
    Similar issue here. We just picked up this machine in the summer has had both A1 and A2 comps replaced by previous company. About a month ago B1 compressor failed and running B2 and B3. We quoted them to replace B1 which we have to shutdown circuit to repair. Now with this A2.01 alarm we gotta fix this issue before we can take b circuit down. Only reason I’m thinking it’s not comp issue is cause it checks good electrically and is not hot to the touch. If sensor was working ohm value would fall below the 4.5k. I will try and run Monday and see what happens keep you posted. Thanks for all the help.

  8. #8
    Join Date
    Dec 2013
    Location
    Russia
    Posts
    203
    Post Likes
    It feels like you have a short circuit. Compare the inductance of the windings of a normal compressor and a dying one.

  9. #9
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Mesahvac. I'm having similar issues with a Carrier 30RBC. What was the outcome of this. Did you condemn the compressor or was it the sensor?

  10. #10
    Join Date
    May 2016
    Location
    Toronto, CAN
    Posts
    154
    Post Likes
    Had that error on similar compressor. Was a bad contactor only putting 165 volts on 1 leg on 208/3. All t contactor were shot and replaced. Have not had an issue since 3 years later.

  11. #11
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    672
    Post Likes
    when changing compressors in a multi compressor refrigerant circuit. Be sure to check for acid before replacing just one.
    One burnt compressor creating acid in the process destroys the other two. And the cycle never ends. Especially if you are not overdoing the clean up process.

    Back top the thermistor. As mentioned of bad contactors. check the run voltage at the compressor. tighten all electrical connections. and be sure its bad and not something goofy.

  12. #12
    Join Date
    Dec 2018
    Location
    Texas
    Posts
    29
    Post Likes
    we have had similar problems in the past with failing/open sensors on the Danfoss compressors, specifically in the AuqaSnap chillers. I usually place a resistor across the sensor and educate the customer on the situation. I hate to sell someone a compressor if its not needed.

  13. #13
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    672
    Post Likes
    I havent had to do this yet. I have not attempted to look it up. Whats the value of the resistor.

    Quote Originally Posted by ChillerTech3384 View Post
    we have had similar problems in the past with failing/open sensors on the Danfoss compressors, specifically in the AuqaSnap chillers. I usually place a resistor across the sensor and educate the customer on the situation. I hate to sell someone a compressor if its not needed.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •