    Dielectric union vs brass adapters

    I have been seeing brass male propress adapters connected to black unions lately. Is this an acceptable practice now? I was always taught to use a dielectric union in this application. This piping is used for boiler hot water.

    Sent from my ASUS_P00J using Tapatalk

  2. #2
    Join Date
    Oct 2012
    Location
    riverside calif
    Posts
    515
    Post Likes
    i will bite , obviously no black pipe being used for the water. I have only seen dielectric unions on the water side.

    and as far as the gas line i believe you can use dissimilar metals.
    Sent from the van with the a/c on.

  3. #3
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,000
    Post Likes
    Not necessary in a closed loop

    Sent from my SM-G960U using Tapatalk

  4. #4
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    106
    Post Likes
    Thread Starter
    Quote Originally Posted by Spitz View Post
    Not necessary in a closed loop

    Sent from my SM-G960U using Tapatalk
    Dielectric unions are not necessary on a closed loop system? All of the commercial sites that I am on use them.
    Is this something specified by engineers or required by code?

    Sent from my VS501 using Tapatalk

  5. #5
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    3,158
    Post Likes
    Lots of different opinions on this. I believe dialectic breaks between copper and steel ARE needed in a closed boiler/chiller system. I have been taught that if using brass fittings between the copper and steel to accomplish this, the brass should be at least 4" long.

    I don't like dielectric unions because they tend to be a weak link that will end up leaking. The brass propress adapter screwed into a black union might not provide a long enough break between the steel and the copper, but it's better than screwing copper right into the steel, and it's probably better than using a dielectric union that has a high possibility of leaking.

    If I were doing it, I would use the black union with a short brass nipple, going to a brass coupling, going to the brass propress male adapter.

    Or I might do the black union with the brass nipple going to a brass propress female adapter, but I try to avoid female adapters if I can help it because they seem to leak often too. The brass propress female adapters are better than normal copper female adapters though. I avoid copper female adapters at all costs whenever possible.

    Another solution would be to incorporate a brass ball valve as the dielectric break. For example, a black threaded union going to a short black nipple going to a threaded brass ball valve with a brass or copper male adapter screwed into it. I think that would be alright too.
    If at First You Don't Succeed, Skydiving Is Not for You.

  6. #6
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    106
    Post Likes
    Thread Starter
    Quote Originally Posted by ammoniadog View Post
    Lots of different opinions on this. I believe dialectic breaks between copper and steel ARE needed in a closed boiler/chiller system. I have been taught that if using brass fittings between the copper and steel to accomplish this, the brass should be at least 4" long.

    I don't like dielectric unions because they tend to be a weak link that will end up leaking. The brass propress adapter screwed into a black union might not provide a long enough break between the steel and the copper, but it's better than screwing copper right into the steel, and it's probably better than using a dielectric union that has a high possibility of leaking.

    If I were doing it, I would use the black union with a short brass nipple, going to a brass coupling, going to the brass propress male adapter.

    Or I might do the black union with the brass nipple going to a brass propress female adapter, but I try to avoid female adapters if I can help it because they seem to leak often too. The brass propress female adapters are better than normal copper female adapters though. I avoid copper female adapters at all costs whenever possible.

    Another solution would be to incorporate a brass ball valve as the dielectric break. For example, a black threaded union going to a short black nipple going to a threaded brass ball valve with a brass or copper male adapter screwed into it. I think that would be alright too.
    Thanks for your info.

    Sent from my VS501 using Tapatalk

  7. #7
    Join Date
    Mar 2015
    Posts
    1
    Post Likes
    I was taught to use dielectric nipples with a brass threaded union in heating water situations.

    Sent from my SM-G965U using Tapatalk