    This is a refrigeration unit that I added a Oil separator to and 2 weeks later I come back and the separator was full of this white wax like substance and drier was plugged. what can it be? I performed triple evacuation on this after oil separator installation.
    Jan 2015
    Iowa
    The wrong oil was used for the application
    Apr 2005
    Australia : Queensland
    Following.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
    In a machine room
    What sort of system? Parallel rack? Single system? What kind of oil and refrigerant?
    Worry is a really gross misuse of one's imagination. -- PHM
    Mar 2015
    Medford, N.Y.
    With all of this waxy stuff in the oil separator, how much oil is in the comp?.How did you determine what was in the oil separator in the 1st place? Did you do an Acid Test?
    Southold, NY
    Besides the oil separator what else has been done to this Rack?
    Jan 2010
    Why did you install a oil separator ?
    Jan 2016
    The triangle in the Keystone
    I had a WIF do this to me a few years ago, minus the oil separator.
    CU would run for a few seconds then cutoff on the LPC. Pressure would slowly build over the next minute or so, comp would kick on and then a few seconds later the LPC would open.
    I had 30 some psi at the outlet of the evap and it never really moved. So I have pressure at the evap but nothing on the roof, must be a clog in this 7/8” suction line. I cut out the trap and blew out these white, waxy, oily slugs.
    That system design didn’t really bring very much oil back to the comp, every inch of horizontal suction line was angled back to the evap and it had gone through three or so compressors in 10 years so I suspected the system was oil logged. I figured all of that played into the wax slugs but I never really knew for sure.
    Mar 2019
    single system Poe r404a
    Mar 2019
    manufacturers recommended since there was a 200ft run
    Mar 2019
    Poe and was originally poe
    Mar 2019
    it's not a rack and nothing else was done it's a new installation 5 months old
    May 2014
    Bay Area California
    New installation with used equipment?
    If you were a real tech, you'd solder a relay on that board and call it good to go.
    I do a triple evac with nitro to remove non condensables.
    I use 56% silver on everything except steel.