Thread: Fujitsu Bacnet Integration

  1. #1
    Join Date
    Sep 2012
    Location
    New York, NY
    Posts
    184
    Post Likes

    Fujitsu Bacnet Integration

    Hi,

    Was tasked with integrating a bunch of Fujitsu Halcyon units using the Fujitsu Bacnet gateway.

    Two issues at hand.

    1 - Space temperature reads 32 degrees on all units.
    2 - The points fail to update after a few days. commands stop writing to stat and status points don't update. The only way to regain communication is to cycle power to units.

    Fujitsu has one guy that knows this and is out on medical leave.

    Thanks,
    Knowledge is money - Ignorance is expensive!!

  2. #2
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    At a guess Intesis might be the company that made the gateway, problem is last I asked for Fujitsu to BACnet they didn't have one.

    https://www.intesisbox.com/en/bacnet/gateways/

  3. #3
    Join Date
    Sep 2012
    Location
    New York, NY
    Posts
    184
    Post Likes
    Thread Starter
    Fujitsu makes one. UTY-VBGX
    So far, its a glorified dumb stat.
    you can change setpoints and unit modes (Heat/Cool/Auto). you can not see space temperature or what the unit is actually doing (cooling/heating).
    Knowledge is money - Ignorance is expensive!!

  4. #4
    Join Date
    Jul 2019
    Location
    MA
    Posts
    1
    Post Likes
    Hello MaxBurn,
    Pleased to share that Intesis is about to release a FJ-AC-BAC-1L unit that will connect to Fujitsu units using connector CN-65 and offer BACnet MS/TP interface.
    This is a 1:1 solution, one interface for every indoor unit head.
    I am the OEM Sales Manager for America at Intesis; please contact me if you have interests.

  5. #5
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    We are interested, you got mail.

  6. #6
    Join Date
    Aug 2019
    Posts
    1
    Post Likes
    I'm in the same boat. We are integrating bunch of Fujitsu Halcyon and Airstage units using BACnet Gateway UTY-ABGX.

    Pretty much the same issues with the exception of space temperature reading 32F. I think the gateway stores the last value of space temperature before it stops responding. The points for Halcyon units fail to update after a few days, commands stop writing to thermostat and status points don't update. But, the points work on Airstage units (even though they're on the same loop). I found the only way to regain communication is to cycle power to units.

    We've had Fujitsu technician on site from across the country about 5-6 times and the issue still remains. Apparently, the Halcyon units are not meant for BACnet integration.

  7. #7
    Join Date
    Aug 2019
    Location
    Sheridan, WY 82801
    Posts
    8
    Post Likes
    But haven't Intesis released the module yet?

  8. #8
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Quote Originally Posted by Jon30 View Post
    But haven't Intesis released the module yet?
    Reach out to the sales guy three posts up, he will explain things.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •