    HVAC System for new addition

    I currently have around 1900sf with a 25 year old Trane Heat Pump. I will be building on an additional 575sf with a bedroom, bathroom, and closet.

    I have got quotes for a new system for the entire house at roughly $$ and for a mini-split system for just the new addition for ~$.

    What is going to be the best way to go on this, considering total cost (purchase price, and electric bill savings)?
    Last edited by beenthere; 03-19-2019 at 04:24 PM.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Adding roughly 20% more Sq Ft of new tight construction shouldn’t need anything extra seeing how most systems are oversized anyway

  3. #3
    Join Date
    Mar 2019
    Posts
    7
    Post Likes
    Thread Starter
    Current heat pump is only 3 ton.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    A complete Manual J and D must be preformed to answer your question.

  5. #5
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Quote Originally Posted by idealtrucks View Post
    Current heat pump is only 3 ton.
    Equipment isn’t sized to square footage.
    Depending on how tight the addition is it could have very little impact on the conditioning needs of the space.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  6. #6
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Adding roughly 20% more Sq Ft of new tight construction shouldn’t need anything extra seeing how most systems are oversized anyway
    Ditto.
    Most systems have more than enough capacity for the house. The duct system is usually too small.
    Do not assume you need a second system.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  7. #7
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Only question is getting the right amount of air to the addition. And if it has a load/loss much different than the rest of the house, it may not be comfy. For example, south or west facing with a lot of windows, may need cooling when the main part doesn't.

    A GOOD dealer can size the main house and addition and see how it would be to get appropriately sized ducts to the addition. Then you can decide.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •