Thread: Three fuses

  1. #1
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes

    Three fuses

    What possible scenario could cause a loss of all three fuses? I replaced the fuses and found no problems.


    It was a 30 ton chiller with four compressors, the number one compressor in A stage was the one with the blown fuses.



  2. #2
    Join Date
    Aug 2013
    Posts
    1
    Post Likes
    Single phase

  3. Likes CEAS-AC-TECH, Core_d liked this post
  4. #3
    Join Date
    Dec 2006
    Location
    phoenix
    Posts
    303
    Post Likes
    Single phase could occur if one fuse blew, causing the other two fuses to draw high current, but it's not normal for both hot TD fuses to fail the same instant. 3 bad fuses is usually a ground. Did you megger the motor and check wiring, connections, etc? More common on 480 volt systems.

  5. Likes CEAS-AC-TECH liked this post
  6. #4
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by tunaguy View Post
    Single phase could occur if one fuse blew, causing the other two fuses to draw high current, but it's not normal for both hot TD fuses to fail the same instant. 3 bad fuses is usually a ground. Did you megger the motor and check wiring, connections, etc? More common on 480 volt systems.
    I have checked everything, and what's the odds that the two remaining time delay fuses blow at the time?

  7. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    If they're drawing too much current, the odds are very high.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. Likes lions_lair liked this post
  9. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Of course anytime a fuse blows you want to be checking the fuse holder. If you're talking about an ancient disconnect, the fuse holders have probably lost their tension on the fuse end caps, and if so, the disconnect should be replaced.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #7
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Of course anytime a fuse blows you want to be checking the fuse holder. If you're talking about an ancient disconnect, the fuse holders have probably lost their tension on the fuse end caps, and if so, the disconnect should be replaced.

    How often have you seen three fuses blow, without a trace of why?


    This unit has a phase monitor, the Carel records events and also has Carel current sensors for each compressor.

  11. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    This can happen when the disconnect holders allow the fuses to overheat when the current is still normal.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. Likes lions_lair liked this post
  13. #9
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    This can happen when the disconnect holders allow the fuses to overheat when the current is still normal.
    No discoloration anyplace on any thing, I spent nearly two hours going over it. Fuses are very tight in the holders, put a megger on the compressor, starter is new, power cable to the compressor is new.


  14. #10
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Sounds like a pretty good mystery.

    It may not have a clear cause.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  15. #11
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,400
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Sounds like a pretty good mystery.

    It may not have a clear cause.
    Fuses, maybe they came from Shenzhen.

  16. #12
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,661
    Post Likes
    Never seen all 3 blow ... nope

  17. Likes The Turtleman liked this post
  18. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,058
    Post Likes
    Everything seems to come from there.....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI