    Hi Everyone. I am new to the site but have been reading a number of threads and am finding them very useful. My background is in construction but I decided to branch out and start installing ductless mini-splits. I completed my first install and performed a 40 minute pressure test @ 250psi. I proceeded to the last step of vacuum pump down and this is where I ran into problems. My vacuum setup is as follows: two Appion core removal tools, an Appion 1/2" vacuum hose and CPS vacuum gage. I pulled down under 500 microns quickly and closed the valve to isolate the vacuum pump from the system. The value immediately went up to several thousand and slow increased so I re-opened the valve and allowed it to pump down awhile longer. After several attempts I got it to remain initially at 400um. It didn't stabilize however and kept creeping up around 20-40um per minute. I wasn't sure if it was my system leaking or my connections so I brought my equipment home to see if I could hold a vacuum with a simplier setup. This setup involved one Appion core removal tool, a vacuum gage, a T-valve and about 3' of 1/4" line with plugged flares. I would post a pic but am too new to do so. This time I pressure tested my setup at 620psi for 24 hours. Pressure was good after 24 hours so I released the nitrogen. I started Pulling a vacuum and again when closing the valve the value would creep up. I don't understand why I can't hold a vacuum after holding 620psi after 24 hours. I am not sure if my vacuum gage is the issue or something else. Anyone have any ideas on what I could try next? Your help is appreciated.

  2. #2
    Join Date
    Mar 2019
    Posts
    3
    Post Likes

    Problem in Vaccum

    Thanks for Sharing the informative post.

  3. #3
    Join Date
    Apr 2010
    Location
    California
    Posts
    503
    Post Likes
    Quote Originally Posted by shaggs2broke View Post
    Anyone have any ideas on what I could try next? Your help is appreciated.
    "Yes I Do". "Your Tools are only as accurate as the last time they were tested and calibrated" When is the last time you "tested and calibrated" your "gages, vacuum pump, and hoses"? Get in the habit of doing this as much as possible.

  4. #4
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    2,913
    Post Likes
    Pump down and pulling a vacuum are two different procedures. If you are pulling a vacuum and the level rises, try pulling the vacuum for a longer time. Also, to test your set up, pull a vacuum on recovery tank; not a length od tubing.
    Doug

  5. #5
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,732
    Post Likes
    Try putting some leaklock on all the fittings. Could also be the core tools are leaking internally. Is this a single head mini and your pulling from both lines? If you only have access to one end of the line length the pressures could just be stabilizing.


    Sent from my iPhone using Tapatalk

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    21,448
    Post Likes
    Quote Originally Posted by shaggs2broke View Post
    Hi Everyone. I am new to the site but have been reading a number of threads and am finding them very useful. My background is in construction but I decided to branch out and start installing ductless mini-splits. I completed my first install and performed a 40 minute pressure test @ 250psi. I proceeded to the last step of vacuum pump down and this is where I ran into problems. My vacuum setup is as follows: two Appion core removal tools, an Appion 1/2" vacuum hose and CPS vacuum gage. I pulled down under 500 microns quickly and closed the valve to isolate the vacuum pump from the system. The value immediately went up to several thousand and slow increased so I re-opened the valve and allowed it to pump down awhile longer. After several attempts I got it to remain initially at 400um. It didn't stabilize however and kept creeping up around 20-40um per minute. I wasn't sure if it was my system leaking or my connections so I brought my equipment home to see if I could hold a vacuum with a simplier setup. This setup involved one Appion core removal tool, a vacuum gage, a T-valve and about 3' of 1/4" line with plugged flares. I would post a pic but am too new to do so. This time I pressure tested my setup at 620psi for 24 hours. Pressure was good after 24 hours so I released the nitrogen. I started Pulling a vacuum and again when closing the valve the value would creep up. I don't understand why I can't hold a vacuum after holding 620psi after 24 hours. I am not sure if my vacuum gage is the issue or something else. Anyone have any ideas on what I could try next? Your help is appreciated.
    Any training, classes, online?

    Where did you purchase this unit?

    Its a waste but at least say your certified!

  7. #7
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,189
    Post Likes
    Most manufacturers state to hold vacuum for 10 minutes under 1000 microns. Sounds like you have achieved that. What ya sweating?

  8. #8
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    10,639
    Post Likes
    Your pressure test is insufficient. Many manufactures call for over 500 PSI for as much as 24 hours.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486

  9. #9
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,732
    Post Likes
    Quote Originally Posted by rider77 View Post
    Your pressure test is insufficient. Many manufactures call for over 500 PSI for as much as 24 hours.
    I doubt thats the case here.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    1,189
    Post Likes
    Quote Originally Posted by rider77 View Post
    Your pressure test is insufficient. Many manufactures call for over 500 PSI for as much as 24 hours.
    That isnt happening in the real world and you know it. Lets be realistic.

  11. #11
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    10,639
    Post Likes
    Quote Originally Posted by Core_d View Post
    I doubt thats the case here.


    Sent from my iPhone using Tapatalk
    No, but doing that low of a pressure test could come back to bite the OP.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486

  12. #12
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    10,639
    Post Likes
    Quote Originally Posted by Adlerberts-Protege View Post
    That isnt happening in the real world and you know it. Lets be realistic.

    I do it.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486

  13. #13
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,732
    Post Likes
    Quote Originally Posted by rider77 View Post
    No, but doing that low of a pressure test could come back to bite the OP.
    I dont do hardly any if any new installs but, my nitro regulator is factory set at 250psi. Some leaks will show up even better with a lower psi.

    Is um a micron? If thats the case he has a dry leak free system.