    High CFM per ton

    Curious running a system with 680CFM per ton (3400CFM on 5 Ton) with a constant full load (60,000BTUs) running a 80F with 60% humidity where everything runs great. The question I have is whether I run the system at 3400CFM or 2000CFM our latent and sensible loads "seem" to remain the same while maintaining the exact same conditions which should not be the case as per the math. Technically by dropping the CFM we should see a major bump in latent but our moisture removal stays consistent at roughly 18 pints per hour whether we drop the CFM or not. What am I missing?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    24,035
    Post Likes
    and who set this up?

  3. #3
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,800
    Post Likes
    Is the system cycling? Keeping it at 80 it may not matter much. Is this a larger system with one compressor down or something? Give us an idea of the scenario here.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    9,262
    Post Likes
    Not enough information. Major infiltration, faulty instruments, incorrect measuring methods, system unable to stabilize due to inconsistent loading.
    Problem I have is your saying they are the exact same conditions when we know that's doubtful. Not doubting you. It's just something might be overlooked.
    I might start with the 3400 cfm. How was that determined.
    Give me a relay with big enough contacts, and I'll run the world!

    You can be anything you want......As long as you don't suck at it.

    If a person wants to create a machine that will be more likely to fail...Make it complicated.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  5. #5
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    9,579
    Post Likes
    How are you determining the outputs and changes?
    Lowering air flow will decrease sensible cooling and increase latetent cooling plus decrease the total capacity of the system.
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  6. Likes Core_d liked this post
  7. #6
    Join Date
    Mar 2016
    Location
    Pahrump, NV
    Posts
    2,178
    Post Likes
    What happens when you go from 2000 CFM to 1500 CFM?

    Did you check the inside of the cabinet for condensate blown off of the coil?
    It's an upside down world we live in.

  8. Likes Core_d liked this post
  9. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,787
    Post Likes
    What is the advantage to the HIGHER CFM???

  10. #8
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,800
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    What is the advantage to the HIGHER CFM???
    Given the information in another current thread its possible the oversized blower acts as a load and extends the run times. We will have to hear from the op though. MrCfm


    Sent from my iPhone using Tapatalk

  11. #9
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    3,397
    Post Likes
    You got some good responses. The main question I have has already been ask but how are you measuring airflow?
    No man can be both ignorant and free.
    Thomas Jefferson

  12. #10
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    6,800
    Post Likes
    Quote Originally Posted by WAYNE3298 View Post
    You got some good responses. The main question I have has already been ask but how are you measuring airflow?
    Its not a ecm blower with dip switches and lights that pushes 3400 cfm. I know that much.


    Sent from my iPhone using Tapatalk

  13. #11
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    9,579
    Post Likes
    Higher cfm = warmer coil=more total cooling capacity=more sensible capacity= less latent capacity=t-stat statisfied quicker
    This is the most important part of setting up an a/c.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  14. #12
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,787
    Post Likes
    Hay,OP,where in the world are you? There is no "change" to the system/structure when going from 3400 CFM down to 2000CFM??

  15. #13
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    9,475
    Post Likes
    I am interested in the equipment. I have never seen 5T equipment that will move 8.5 ton of air. If the charge was set with 3400 CFM then it can't be right at 2000.