    EasyIO OEM controller move from RS485 toIP?

    I am servicing a site that has several SCU units with OEM installed EASYIO FG32 controllers tied into the mstp bus with a numbered of Distech ECB VAV. Ive got an existing IP bus that runs throughout the mechanical rooms and Id like to see if its possible to to change the device to an IP controller, do I just needed to change IP address and devices ID?
    Thanks

  2. #2
    Join Date
    May 2006
    Location
    Greater Atlanta Area
    Posts
    598
    Post Likes
    Yes they can communicate on both at the same time

    Sent from my VS988 using Tapatalk

  3. #3
    Join Date
    Feb 2008
    Location
    Purcellville Va.
    Posts
    938
    Post Likes
    Thread Starter
    These units have an android tablet talking to a Hotspot plugged into the ethernet port.
    Can I change the IP address from the tablet? One of the user guides I found online says I need the Sedona tools to change the IP?

  4. #4
    Join Date
    May 2006
    Location
    Greater Atlanta Area
    Posts
    598
    Post Likes
    Quote Originally Posted by 381engineer View Post
    These units have an android tablet talking to a Hotspot plugged into the ethernet port.
    Can I change the IP address from the tablet? One of the user guides I found online says I need the Sedona tools to change the IP?
    You need the cpt programming tool to change the ip configuration

    Sent from my VS988 using Tapatalk