    Mar 2016
    will using existing 6" B vent cause problems
    has anyone ever had a problem increasing to the next size common B vent example Table says 5" common vent will satisfy, will the existing 6" B vent also satisfy? or cause condensation ?
    80K Furnace with 32K water heater type B connectors 18 feet tall Height 3' rise
    Virginia
    Quote Originally Posted by uncle matt View Post
    Going strictly by the tables it shouldn’t be an issue, but please note, the venting tables do not guarantee the appliances will vent properly. The tables are simply computer calculations, and not empirical data, from actual tests in a lab under varying conditions.
    The disclaimer on the venting tables states:
    Neither the Gas Research Institute (GRI), members of GRI, nor any person acting on behalf of either, makes any warranty or representation, express or implied, with respect to the accuracy, completeness, or usefulness of this information…………….
    Only measuring draft, draft interference and seeing STABLE CO and O2 numbers from a combustion test will confirm proper venting.
    Cincinnati, Ohio
    In reality you are less likely to condense in 6" B-vent than in 5".
    captain CO
    Jan 2010
    CT
    Check the code.
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR