Thread: TXV for R407C

  1. #1
    Join Date
    May 2009
    Location
    Earth
    Posts
    8,734
    Post Likes

    TXV for R407C

    Should we be up sizing replacement TXVs for R22 systems that will be converted to R407C? I have a 10 ton Trane Split system that needs a new TXV, and was wondering if I should go bigger to get around the capacity loss?

  2. #2
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    2,521
    Post Likes
    Don’t think it works that way, because that doesn’t change the evap or condenser size
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  3. #3
    Join Date
    May 2009
    Location
    Earth
    Posts
    8,734
    Post Likes
    Thread Starter
    I thought R407C needed more flow then 22?

    According to a United book, multiply by 1.07.

    10x1.07=10.7 ton valve for R407C

  4. #4
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    That is the nominal tonnage rating. More calculations needed to figure out actual required tonnage.
    Quote Originally Posted by EugeneTheJeep View Post
    I thought R407C needed more flow then 22?

    According to a United book, multiply by 1.07.

    10x1.07=10.7 ton valve for R407C
    Sent from my SM-G965W using Tapatalk

  5. #5
    Join Date
    May 2009
    Location
    Earth
    Posts
    8,734
    Post Likes
    Thread Starter
    Actually Sporlan TXVs are 10% oversize, so I guess not a problem.

  6. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,438
    Post Likes
    I’ve never heard that 407 requires more flow.

    Are you talking about cubic feet per minute of refrigerant flow through the compressor / system?

    Of course the specific gravity is different than 22, so you would install less Than the original factory charge on a retrofit.

  7. #7
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    You should be fine with the same valve. The capacity difference is negligible.

    Sent from my Moto Z (2) using Tapatalk

  8. #8
    Join Date
    Jul 2014
    Posts
    117
    Post Likes
    you have to see how much capacity unit will loos by changing the to R407 the use a txv for that size, TVX usually can work on 70% of rate capacity with no problem, but try be as closer as posiblem in my experiance with Trane TXV, they normally have bigger capacity than a universal TXV from Danfost, You can used a 12 ton TXV that can go down up to 8.5 tons.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •