    I have a walk-in low -temp freezer (10'x12'x 8') that is forming ice on the ceiling and I can't quite figure out why. Defrost cycle seems to be be working fine as well as the fan delay after the defrost cycle terminates. The one theory I have is that the users will prop the door open and turn the unit off a couple of times a week for up toan hour or so to either stock or inventory. It is just off of the kitchen and I am guessing that the warm humid air is accumulating at the ceiling them forming water droplets. Any other ideas or suggestions? Thanks

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,899
    Post Likes
    That's a good possibility.

    how are they shutting it down?

  3. #3
    Join Date
    Aug 2012
    Posts
    54
    Post Likes
    Thread Starter
    Shutting off the disconnect. I have talked with them about this and they won’t stop doing it. I have talked with them about shutting it down at the thermostat but that seems to be too hard for them to do. Would shutting this down without pump down contribute to this problem?

  4. #4
    Join Date
    Aug 2012
    Posts
    54
    Post Likes
    Thread Starter
    Also did not put in my first post that the the evapotator drain is clear and drains during defrost.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,899
    Post Likes
    we install a switch behind the blower that breaks the N wire so heaters, fans and solenoid are off. Unfortunately any frost on the blower will begin to defrost and once they turn the switch on it gets blown off. I believe this is what your experiencing.

    One problem with shutting off the disconnect is it kills the crankcase heater, that can lead to other problems.

  6. #6
    Join Date
    Aug 2012
    Posts
    54
    Post Likes
    Thread Starter
    So by doing that then the fans imediatly shut down and then the condenser will pump down and shut off. Correct? I think I will try this and see if it helps.

  7. #7
    Join Date
    Jan 2010
    Posts
    19,356
    Post Likes
    If your defrost heaters don't terminate on a switch and are on the timer you could create steam.

  8. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,899
    Post Likes
    Quote Originally Posted by VTP99 View Post
    If your defrost heaters don't terminate on a switch and are on the timer you could create steam.
    That's why we break the N!

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,899
    Post Likes
    Quote Originally Posted by tomnkc View Post
    So by doing that then the fans imediatly shut down and then the condenser will pump down and shut off. Correct? I think I will try this and see if it helps.
    If there's water on the coil it will still blow off. W I Freezers should be inside W I Coolers that helps but the icing can still appear. The only true solution is NOT shutting it down!

  10. #10
    Join Date
    Jan 2010
    Posts
    19,356
    Post Likes
    Quote Originally Posted by pecmsg View Post
    That's why we break the N!
    I was referring to normal operation ( or lack of )
    In a defrost mode the heaters are steaming the water left on the coil.

  11. #11
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,939
    Post Likes
    I had this problem once, with workers in a hot kitchen blocking service the freezer door open. Caused all sorts of icing problems. Owner of the restaurant tried to fix the problem but the kitchen staff kept it up when he wasn’t there.
    I wired in a timer door switch connected to a horn above the ceiling. After 3 continuous minutes of the door being open the horn went off until the door was closed. After a week we never had that problem again.
    Also check the drain. An untrapped freezer drain will draw humidity/moisture back into the freezer if terminated in a humid/wet area.
    ďI havenít failed. Iíve just found 10,000 ways that wonít work.Ē - Thomas Edison

    ďItís not whether you get knocked down, itís whether you get up.Ē - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  12. #12
    Join Date
    Aug 2012
    Posts
    54
    Post Likes
    Thread Starter
    I thought about that. The drain is not trapped and terminates to the outside. In addition to the kill switch I think I will add a trap. As far as the horn goes that would be a no go. This is in a school district and come Hell or High water they are going to turn this off when they are in there. I just want to cover all my bases before I tell them that if they don’t stop the practice nothing will change. The real issue for them is not the ice on the ceiling but when they are in there long enough it melts and drips water on the floor then refreezes causing a slip/ fall issue. Thanks everyone for your help with this.

  13. #13
    Join Date
    Jun 2006
    Posts
    681
    Post Likes
    Quote Originally Posted by rider77 View Post
    Also check the drain. An untrapped freezer drain will draw humidity/moisture back into the freezer if terminated in a humid/wet area.
    I have heard this for 30 years. Worked on many WIF without trapped drains. Never seen it cause an issue.

    That's just me though. YMMV.

  14. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,899
    Post Likes
    Quote Originally Posted by stat View Post
    I have heard this for 30 years. Worked on many WIF without trapped drains. Never seen it cause an issue.

    That's just me though. YMMV.
    I've seen it on a few occasions! Agreed not many but it can happen.

  15. #15
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,939
    Post Likes
    Quote Originally Posted by stat View Post
    I have heard this for 30 years. Worked on many WIF without trapped drains. Never seen it cause an issue.

    That's just me though. YMMV.
    Ever wonder why freezers have heated vents? Itís to avoid drawing a negative pressure on the box when the door is opened and warm air rushes in, then is quickly cooled and thus takes up less volume. Freezers tend to be their own little low pressure zones if you will.
    At an extreme case, I had a box located outdoors that had an untrapped drain. It would pull humidity in so bad it would build ice on the fan guards and either freeze the blades in place or break them altogether.
    ďI havenít failed. Iíve just found 10,000 ways that wonít work.Ē - Thomas Edison

    ďItís not whether you get knocked down, itís whether you get up.Ē - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  16. #16
    Join Date
    Jan 2010
    Posts
    19,356
    Post Likes
    The heated vent is on the vacuum breaker.
    This breaks the inside vacuum when one reopens a resentally closed door.

  17. #17
    Join Date
    Aug 2009
    Location
    Bracebridge, ON
    Posts
    90
    Post Likes
    I'm with VTP99, check that there is defrost termination, and that it is terminating correctly.
    When you are dead, you do not know that you are dead. All of the pain is felt by others.
    The same thing happens when you are stupid.

  18. #18
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    2,164
    Post Likes
    Outdoor box? Leaking roof?

  19. #19
    Join Date
    Aug 2018
    Location
    Madison, WI
    Posts
    34
    Post Likes
    Quote Originally Posted by tomnkc View Post
    ...The real issue for them is not the ice on the ceiling but when they are in there long enough it melts and drips water on the floor then refreezes causing a slip/ fall issue. Thanks everyone for your help with this.
    If their concern is ice on the floor, I sell desiccant dehumidifiers that will sublimate that up. I will be the first to admit that its a band-aid to fix stupid behavior but if they can't train the people...it will solve the issue.

  20. #20
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,284
    Post Likes
    Quote Originally Posted by rider77 View Post
    An untrapped freezer drain will draw humidity/moisture back into the freezer if terminated in a humid/wet area.
    Iíve seen this several times. Generally more of a summer time issue when the fans are drawing in outdoor hot/humid air. The worst Iíve seen was a freezer drain that terminated into a floor drain which was shared by two steamers. Neither steamer had a drain tempering kit and there was always a steady stream of HOT water going down the drain. That walk-in looked like a blizzard had just passed through it.