Results 1 to 20 of 28
Thread: Ice on the ceiling of a walk in
    Aug 2012
    I have a walk-in low -temp freezer (10'x12'x 8') that is forming ice on the ceiling and I can't quite figure out why. Defrost cycle seems to be be working fine as well as the fan delay after the defrost cycle terminates. The one theory I have is that the users will prop the door open and turn the unit off a couple of times a week for up toan hour or so to either stock or inventory. It is just off of the kitchen and I am guessing that the warm humid air is accumulating at the ceiling them forming water droplets. Any other ideas or suggestions? Thanks
    Southold, NY
    That's a good possibility.
    how are they shutting it down?
    Aug 2012
    Shutting off the disconnect. I have talked with them about this and they won’t stop doing it. I have talked with them about shutting it down at the thermostat but that seems to be too hard for them to do. Would shutting this down without pump down contribute to this problem?
    Aug 2012
    Also did not put in my first post that the the evapotator drain is clear and drains during defrost.
    Southold, NY
    we install a switch behind the blower that breaks the N wire so heaters, fans and solenoid are off. Unfortunately any frost on the blower will begin to defrost and once they turn the switch on it gets blown off. I believe this is what your experiencing.
    One problem with shutting off the disconnect is it kills the crankcase heater, that can lead to other problems.
    Aug 2012
    So by doing that then the fans imediatly shut down and then the condenser will pump down and shut off. Correct? I think I will try this and see if it helps.
    Jan 2010
    If your defrost heaters don't terminate on a switch and are on the timer you could create steam.
    Southold, NY
    That's why we break the N!
    Southold, NY
    Quote Originally Posted by tomnkc View Post
    If there's water on the coil it will still blow off. W I Freezers should be inside W I Coolers that helps but the icing can still appear. The only true solution is NOT shutting it down!
    Jan 2010
    I was referring to normal operation ( or lack of )
    In a defrost mode the heaters are steaming the water left on the coil.
    Jun 2014
    Dover, DE
    I had this problem once, with workers in a hot kitchen blocking service the freezer door open. Caused all sorts of icing problems. Owner of the restaurant tried to fix the problem but the kitchen staff kept it up when he wasn’t there.
    I wired in a timer door switch connected to a horn above the ceiling. After 3 continuous minutes of the door being open the horn went off until the door was closed. After a week we never had that problem again.
    Also check the drain. An untrapped freezer drain will draw humidity/moisture back into the freezer if terminated in a humid/wet area.
    ďI havenít failed. Iíve just found 10,000 ways that wonít work.Ē - Thomas Edison
    ďItís not whether you get knocked down, itís whether you get up.Ē - Vince Lombardi
    Aug 2012
    I thought about that. The drain is not trapped and terminates to the outside. In addition to the kill switch I think I will add a trap. As far as the horn goes that would be a no go. This is in a school district and come Hell or High water they are going to turn this off when they are in there. I just want to cover all my bases before I tell them that if they don’t stop the practice nothing will change. The real issue for them is not the ice on the ceiling but when they are in there long enough it melts and drips water on the floor then refreezes causing a slip/ fall issue. Thanks everyone for your help with this.
    Jun 2006
    Quote Originally Posted by rider77 View Post
    I have heard this for 30 years. Worked on many WIF without trapped drains. Never seen it cause an issue.
    That's just me though. YMMV.
  14. #14
    Southold, NY
    Quote Originally Posted by stat View Post
    I've seen it on a few occasions! Agreed not many but it can happen.
  15. #15
    Jun 2014
    Dover, DE
    Ever wonder why freezers have heated vents? Itís to avoid drawing a negative pressure on the box when the door is opened and warm air rushes in, then is quickly cooled and thus takes up less volume. Freezers tend to be their own little low pressure zones if you will.
    At an extreme case, I had a box located outdoors that had an untrapped drain. It would pull humidity in so bad it would build ice on the fan guards and either freeze the blades in place or break them altogether.
  16. #16
    Jan 2010
    The heated vent is on the vacuum breaker.
    This breaks the inside vacuum when one reopens a resentally closed door.
  17. #17
    Aug 2009
    Bracebridge, ON
    I'm with VTP99, check that there is defrost termination, and that it is terminating correctly.
    When you are dead, you do not know that you are dead. All of the pain is felt by others.
    The same thing happens when you are stupid.
  18. #18
    Jun 2012
    Northern NV
    Outdoor box? Leaking roof?
  19. #19
    Aug 2018
    Madison, WI
    ...The real issue for them is not the ice on the ceiling but when they are in there long enough it melts and drips water on the floor then refreezes causing a slip/ fall issue. Thanks everyone for your help with this.
    If their concern is ice on the floor, I sell desiccant dehumidifiers that will sublimate that up. I will be the first to admit that its a band-aid to fix stupid behavior but if they can't train the people...it will solve the issue.
  20. #20
    Jan 2016
    The triangle in the Keystone
    Iíve seen this several times. Generally more of a summer time issue when the fans are drawing in outdoor hot/humid air. The worst Iíve seen was a freezer drain that terminated into a floor drain which was shared by two steamers. Neither steamer had a drain tempering kit and there was always a steady stream of HOT water going down the drain. That walk-in looked like a blizzard had just passed through it.