    FX-Jace Numeric writeable not accepting commands

    Having issues with some setpoints in a PCV-1630 not allowing setpoint changes to the points mapped into the FX-Jace running 4.2 software. The points are under the Balancer Override SD primitive in PCT. The mapped points are CLG-MAXFLOW, CLGOCC-MINFLOW, HTGOCC-MINFLOW, SA-AREA, and SA-KFACTOR. They are mapped as Numeric writeable, but turn orange when commanded and show as not writeable.



    Any help with this issue would be greatly appreciated.


    Thanks

  2. #2
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    1,162
    Post Likes
    It sounds like they are not set up as Network Inputs in the PCV. In the Jace, instead of writing to Present Value on the numeric writeable, change the attribute to 3113 and see if it writes then.

  3. Likes bolt950rider liked this post.
  4. #3
    Join Date
    May 2014
    Posts
    14
    Post Likes
    Thread Starter
    Thank you. Using 3113 worked great! Have to change the point to writeable first then enter 3113 on top of the present value box.

  5. #4
    Join Date
    Mar 2018
    Posts
    181
    Post Likes
    That should be writing to the relinquish default value, either you can look through the drop down menu of the points properties, or when you discover points, hit the +next to a point and grab the relinquish default point/match it to the one you brought in already.


    Sent from my iPhone using Tapatalk