    Annual energy consumption

    Hi everyone,

    In the Ashrae book, the annual heating consumption formula is:
    Q = 24*q*HDD/n*(Tin – Tout)

    Q = Annual energy consumption
    q = Heating gain (Btuh)
    HDD = Heating degree days
    n = Efficiency
    Tin = Indoor temperature (Balance temperature) in F
    Tout = Outdoor temperature in F

    For example: If my heating unit capacity is 75000 Btuh, my indoor temperature is 72 F and my seasonal outdoor temperature is 20 F, HDD is 4500 and the efficiency is 0.9
    My annual energy consumption is: 173 077 kBtuh

    If I decrease my indoor temperature at 70F, my annual energy consumption increase at 180 000 kBtuh.

    We are supposed to have lower annual consumption by decreasing indoor temperature, right?
    If not, can you correct my reasoning?

    Thank you in advance !

  2. #2
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    No volunteers to help me?

  3. #3
    Join Date
    Jan 2019
    Location
    In Front Of A Computer
    Posts
    24
    Post Likes
    I don't have the ASHRAE book in front of me to verify, but looking at the units, they don't quite pencil out.

    q is BTU/hr (rate of change of heat)
    HDD is days > the 24 is to convert from hours to day
    T is °F

    Using your equation, the units for Q would be BTU/°F.

  4. #4
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    Hello BASengineer,
    Thank you for the reply and the correction of Q units. Good point.
    My question is about the annual energy cosumption who increase with the decrease of DT and vice versa.

    Have you an idea? If is it the correct formula to estimate the energy consumption?

    Best regards !

  5. #5
    Join Date
    Nov 2001
    Posts
    125
    Post Likes
    I agree with @Malmo. That equation does not make sense. Which ASHRAE book is it from? Can you post screenshot of the page?

  6. #6
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    Hello coolcoil,

    I try to post a screenshot. It's my first time to post a
    picture later.

  7. #7
    Join Date
    Jan 2019
    Location
    In Front Of A Computer
    Posts
    24
    Post Likes
    Quote Originally Posted by Malmo View Post
    Hello BASengineer,
    Thank you for the reply and the correction of Q units. Good point.
    My question is about the annual energy cosumption who increase with the decrease of DT and vice versa.

    Have you an idea? If is it the correct formula to estimate the energy consumption?

    Best regards !
    I looked it into a little bit further, as it's been a while since I've had to deal with degree days.

    So HDD units are actually °F. See https://www.e-education.psu.edu/egee102/node/2076. That cancels out the units from (Tin - Tout). I apologize for the misinformation of the HDD units being days.

    q is correct as Btu/hr. Q will result in Btu/hr as well, which can be converted to kW (1 kW = 3412.1 Btu/hr).

    If you can post a screenshot of that section of the ASHRAE book or have the chapter, that'd be helpful.

  8. #8
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    Thank you for this informations. I haven't a problem with the units but the sens of the formula.
    In the Ashrae Booke "Fundamental" 2013. 31st Chapter.
    I will post a screenshot later, I have difficulties to insert a picture with my ipad.

    Thank you !

  9. #9
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    This is a screenshot of the formula from the fundamental of ashrae book

    [IMG][/IMG]

  10. #10
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    Ktot = Heat loss coefficient
    Attached Images Attached Images  

  11. #11
    Join Date
    Jul 2014
    Posts
    299
    Post Likes
    Another way to look at it is to start with Newton's Law of Cooling. For a flat surface:
    Btu/hr = U x A x (delta T), where U = heat transfer coefficient (btu/ft2-hr-F) and A is the area (ft2)

    Annual BTU from Degree Days: BTU = U x A x DD x 24hrs/day

    From Newton's Law: U x A = Btuh/(delta T). Substituting into the Annual BTU equation:
    BTU = [Btuh/(delta T)] x DD x 24hrs/day

    This appears to be the same as:
    Q = 24*q*HDD/n*(Tin-Tout) (with the addition of efficiency)

    I've seen the transfer equations many times, but this is new twist in looking at it. Sort of an 'inverse modeling' approach since you have the heating unit capacity (btuh).

    Attached is my current CEM "Cheat Sheet".
    Attached Images Attached Images

  12. #12
    Join Date
    Jun 2018
    Posts
    14
    Post Likes
    Thread Starter
    Hi tridiumtec.

    Thank you for your reply, it's exactly the same understanding that I had.
    However, I find contradictory the fact that the energy consumption is inversely proportional with the temperature differential.

  13. #13
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    9,040
    Post Likes
    Just adding as far as checking the formula, ASHRAE has a correction sheet in their books for corrections after publication. Not sayin the Gods have failed, probably the publisher.
    Give me a relay with big enough contacts, and I'll run the world!

    You can be anything you want......As long as you don't suck at it.

    If a person wants to create a machine that will be more likely to fail...Make it complicated.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •