    Alerton VLC Question

    Been about 12 years since I worked on Alerton and I've been tasked with calibrating all of the space sensors in a school. I have access to all the VLC DDC programs but I can't remember how to apply an offset to an AI. Can anyone help? TIA

  2. #2
    Join Date
    Nov 2018
    Location
    Los Angeles, CA
    Posts
    46
    Post Likes
    You need to transfer the AI to an AV point with the desired offset. Say for example the space temp is what you are calibrating for a microset. You would place an add block with the desired calibration offset to AV-101 (this is the temp that is displayed on the digital readout of the thermostat if it has one). This means you will need to update all your graphics to reference your new AV points as well if they were displaying the AI.