    Quote Originally Posted by navyguy1 View Post
    Ok. 500 microns or better ok with or without triple evacuating?
    I would go down to around 200 microns, such a small unit should evacuate extremely quickly

    some people say 200, some say 300, some say 500 .... I would go 200

    try not to leave the system exposed to the atmosphere while swapping compressors, tape or seal the lines until brazing back together to prevent moisture from entering the system and getting into POE oil
    "All that is necessary for the triumph of evil is that good men do nothing." (Edmund Burke)

  2. #15
    Join Date
    Jun 2006
    Posts
    1,138
    Post Likes
    Dead comp, get the cap tt hh and i strongly r3comend doing the cap tube as well.

    Big fan of sporlan for good reason, 30 years of good luck and observed issues with others when supplied by warranty.

  3. #16
    Join Date
    Dec 2018
    Location
    Ventura, CA
    Posts
    22
    Post Likes
    Thread Starter
    Thanks all for the great advice. Ill put in an order for a few LLFD so ill be ready for the next one.