    Danfoss VFD

    York make up air
    Model : Z34M5IANEH0001A
    Serial: N1N3319796

    System disconnect off on arrival,start up 3 of the compressors turn on and ODF kicks on but no blower, check in and see the VFD screen is blank. Do a reset and LCD screen is back, still no blower and getting alarm 7 - dc overvoltage , I followed the few troubleshooting tips I could from the manul, not sure what connecting a brake resistor would do? , just wondering if anyone has seen this or are familiar with VFD's. Going back tomorrow and calling Tech support but, just want to see if I can't get some info before hand , thanks!

  2. #2
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,269
    Post Likes
    Have you don a serch for a danfoss service manual?

  3. #3
    Join Date
    Feb 2006
    Location
    Where the wind comes sweeping down the plains
    Posts
    513
    Post Likes
    Not sure which model you have, but out of my Trane TR200 manual (equal to VLT-6000 I believe), it says...
    "If the intermediate circuit voltage exceeds the limit, the frequency converter trips after a time.
    Troubleshooting:
    Extend the ramp time
    Change the ramp type
    Activate functions in par.2-10 Brake Functions
    Increase par.14-26 Trip Delay at Inverter Fault"

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •