    Sizing

    First off I am a new member.
    I have 12.5 ton unit supply a commercial building that was wide open. The tenants have now decided to try an lease it out and need ducting through out. The total square footage of the building is 3400' with 12 ceilings that are now going to be 8' ceilings through out with ceiling tile. I am trying to distribute according to room size but am running into an extra 1500cfm. How should I approach this?

  2. #2
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    7,597
    Post Likes
    You need to size by room load not size. You can have 2 rooms both 1000 sq ft and because of a variety of conditions one can take twice as much air as the other, or they may both be the same.

  3. Likes Metalman0880 liked this post
  4. #3
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    20,044
    Post Likes
    If you are distributing to room size, then you will never have anything left over.


    Quote Originally Posted by Bringtheheat View Post
    First off I am a new member.
    I have 12.5 ton unit supply a commercial building that was wide open. The tenants have now decided to try an lease it out and need ducting through out. The total square footage of the building is 3400' with 12 ceilings that are now going to be 8' ceilings through out with ceiling tile. I am trying to distribute according to room size but am running into an extra 1500cfm. How should I approach this?
    [Could this be another PSE trap?]
    If you were a real tech, you'd solder a relay on that board and call it good to go.

    I do a triple evac with nitro to remove non condensables.

  5. Likes HVAC_Marc liked this post
  6. #4
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,796
    Post Likes
    ~ Waves at PSE ~

    Sent from my SM-G965W using Tapatalk

  7. #5
    Join Date
    Nov 2008
    Location
    Long Island NY
    Posts
    862
    Post Likes
    Lol, definitely not PSE.

    Sent from my SM-G965U using Tapatalk

  8. #6
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    20,044
    Post Likes
    How so? Did he get incarcerated?
    If you were a real tech, you'd solder a relay on that board and call it good to go.

    I do a triple evac with nitro to remove non condensables.

  9. #7
    Join Date
    Nov 2008
    Location
    Long Island NY
    Posts
    862
    Post Likes
    I speak with him time to time. Plus the OP gave too much info, whereas PSE doesn't.

    Sent from my SM-G965U using Tapatalk

  10. Likes HVAC_Marc liked this post
  11. #8
    Join Date
    Feb 2019
    Posts
    2
    Post Likes
    Thread Starter
    I would say most the rooms are the same except for the one the contains the windows and another that has an exterior wall.

  12. #9
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    21,628
    Post Likes
    push all the extra into those rooms. it's the hack way. it'll be fine.

  13. #10
    Join Date
    Jan 2010
    Posts
    15,269
    Post Likes
    And what is the return air plan ?

  14. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    76,802
    Post Likes
    Quote Originally Posted by Bringtheheat View Post
    First off I am a new member.
    I have 12.5 ton unit supply a commercial building that was wide open. The tenants have now decided to try an lease it out and need ducting through out. The total square footage of the building is 3400' with 12 ceilings that are now going to be 8' ceilings through out with ceiling tile. I am trying to distribute according to room size but am running into an extra 1500cfm. How should I approach this?
    Manual N.

    I think your forgetting to allow for the number of people, fresh air, and lighting heat gain.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.