    Rectangular Tee 45 Degree Diverging branch, SMACNA OR ASHRAE?

    I have just realized a huge difference in Loss coefficients values between SMACNA's Table 14-14 N, and ASHRAE's SR5-13, Rectangular Tee 45 degree diverging branch. ASHRAE seems to have much higher coefficient values for a given flow rate ratio (Qb/Qc).

    Which standard do you recommend I follow?

    Thanks,
    Baradei

  2. #2
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Maybe one has turning vanes and the other doesn't. Or long sweep vs short. There's likely a difference somewhere.
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  3. #3
    Join Date
    Mar 2015
    Location
    Tx
    Posts
    1,951
    Post Likes
    I allways used SMACNA only because every plan/spec job I did required a SMACNA Duct Construction manual be with us on the job. Yes did get asked to see it on one job & only one.

  4. #4
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    14,090
    Post Likes
    Quote Originally Posted by oldguy1949 View Post
    I allways used SMACNA only because every plan/spec job I did required a SMACNA Duct Construction manual be with us on the job. Yes did get asked to see it on one job & only one.
    Who required this?
    We are here on Earth to fart around ......Kurt Vonnegut

    You can be anything you want......As long as you don't suck at it.

    USAF 98 Bomb Wing 1960-66 SMW Lu49

  5. #5
    Join Date
    Mar 2015
    Location
    Tx
    Posts
    1,951
    Post Likes
    Quote Originally Posted by hvacker View Post
    Who required this?
    Written in the specs by the engineer/architect. You allways read the specs before bidding don't you ? On a school job that had 3 suspended air handlers the engineer buried the spec on the safety drain pans in the book & not on the plans ,had to be 20 gauge or thicker & the sob actually got on a ladder with a sheetmetal guage when doing the final inspection.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •