    Shut off switch on HTP tank

    I have a newer HTP indirect water tank. There is a switch installed that is supposed to turn off the call for heat, it's basically a thermostat wire with an on/off switch. However even when the switch is off, the tank keep heating the water. One end of the wire goes into the panel on the tank, the other end goes into the TACO box on the wall. If I flip the switch on, I do see a zone activate and I can hear something happening in the tank. But - even after a week with the switch clearly off and then 7+ showers later the water was still very hot and the H pipe on top is also very hot (too hot to hold for more than a second).

    ANy ideas on why the switch would not work? Maybe it's not wired correctly into the tank and the tank defaults to calling for heat?

    I know I can just turn down the dial on top, but this is a seasonal house and I wanted to convert that manual switch to a smart switch so I can turn the water on and off remotely before and after short term renters arrive.

    Thanks in advance!
    Frank

  2. #2
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    2,369
    Post Likes
    Sounds to me like a few possibilities or a combination of:
    -A thermostat wire from the aquastat on the indirect to the Taco zone control is shorted or pinched, calling the indirect.
    -The aquastat on the indirect is defective (least likely but possible)
    -The zone control is defective, easily checked by a qualified tech.
    -Either a flow check is missing, the indirect is piped incorrectly (not trapped), or if it's controlled by a zone valve or circulator, that needs to be checked also.
    This is easy troubleshooting with the right knowledge and a meter by a qualified tech.
    Uh...Google it yourself!

  3. #3
    Join Date
    Jan 2011
    Posts
    26
    Post Likes
    Thread Starter
    Thanks for the reply. The odd thing is when I flip the switch on I see the zone on the taco go on right away and I hear something kick on in the tank. But even with it off it just keeps heating the water....

  4. #4
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    2,883
    Post Likes
    There is hot water from the boiler going to the tank when it's not supposed to. From your description it probably has nothing to do with the switch. I'm guessing you could probably turn the setting on the tank all the way down and the water is going to be hot all the time.

    You're going to have to get a hydronics tech in to check the system over and find out why the tank is being heated when it's not supposed to be.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.