    Metasys VMA1630

    Can I use a VMA1630, to utilize the integrated pressure sensor, without using the integrated actuator?

  2. #2
    Join Date
    Sep 2007
    Location
    Kenilworth NJ
    Posts
    1,121
    Post Likes
    Quote Originally Posted by Hunterseg View Post
    Can I use a VMA1630, to utilize the integrated pressure sensor, without using the integrated actuator?
    Sure, just dont tighten the actuator clamp onto anything.... I might be missing the thrust of what you're asking...maybe more details are needed.
    Hmmmm....smells like numbatwo to me.

  3. #3
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,753
    Post Likes
    Hunterseg,
    The VMA1630 has a built in actuator so you simply de-select the "Integrated Actuator" in the Q & A in CCT.
    Maybe you should consider the VMA1628 or PCV1628 that do not have the built in actuator.
    If sense were so common everyone would have it !
    Stupid should Hurt !
    If people took care of their cars like they do their HVAC Systems you'd see a lot more people walking
    !

  4. #4
    Join Date
    Jun 2016
    Location
    Saavannah GA
    Posts
    8
    Post Likes
    I once needed just one more AI point, so I stuck an old VMA1420 I had laying around in a VAV box enclosure next to the one running the box.