    Quote Originally Posted by pecmsg View Post
    I certainly hope your right but phase reversal shouldn't cause that.

    Last time i saw those fuses blow the electrician zip tied the N wire to the heater.
    Is is common for the fan wires to rub out on the fan mounting brackets.
    I checked out all the fan wires. Replaced fan delay. Everything checked out. Reversed the legs and it’s been going since the day after my original post

  2. #41
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,796
    Post Likes
    Quote Originally Posted by raglegacy View Post
    I checked out all the fan wires. Replaced fan delay. Everything checked out. Reversed the legs and it’s been going since the day after my original post
    OK

    All im saying is the control circuit is Single Phase. Doesn't mater L1, 2 or 3

    Compressor rotation yes especially with scrolls.

    Youll be back

  3. #42
    Join Date
    Jan 2010
    Posts
    15,806
    Post Likes
    Only time I've seen a resolve like that was with a delta corner grounded b phase service.
    I replaced a single phase blower motor and it kept pulling high amps.
    I moved the one lead off that b phase and the amps fell in line.

  4. #43
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,796
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Only time I've seen a resolve like that was with a delta corner grounded b phase service.
    I replaced a single phase blower motor and it kept pulling high amps.
    I moved the one lead off that b phase and the amps fell in line.

  5. #44
    Join Date
    Jan 2010
    Posts
    15,806
    Post Likes
    Quote Originally Posted by pecmsg View Post
    OK

    All im saying is the control circuit is Single Phase. Doesn't mater L1, 2 or 3

    Compressor rotation yes especially with scrolls.

    Youll be back
    I agree and think by chance with all the moving of wires around to find a cause might have temporarily fixed the issue.
    That circuit only has a crank case heater ( via a aux ) and a low / high pressure switch in play. Unless it's got the oil options.