    Quote Originally Posted by garyed View Post
    What you're forgetting is the static pressure is usually based on 100 ft. of duct length. If you try to move 800 CFM through 100 ft. of 12" flex then your static is going to be high like around 2.5 but if you're moving it through only 20ft. of duct its going to be around .05. Your velocity doesn't change so you're still going to be around 1000 fpm but the shorter length is what gives you less friction.
    Help me understand this, you can move 1000 fpm velocity through 20ft of 12” duct at .05 static but at 100ft same size and same velocity I have .25” static?(you did mean .25 and not 2.5 correct?).

    Say if i have 100’ of 12” duct and i measure .05” static at the outlet of the duct with the grill removed am i moving 380cfm at less than 500fpm?

    Or do i need to measure the static pressure drop between inlet and outlet, total equivalent length of duct, diameter of duct and FPM to determine CFM?

    Ductulators and duct curve charts are not “friction charts” they are really FRICTION LOSS CHARTS.

    After reading your post im a bit confused as to how to use this info for practical purposes and what measurements need to be taken to determine what.

    Using TESP and a fan curve chart is easy enough and sizing a duct using a ductulator and a standard .01 friction loss is easy enough but i guess i lack the real intimate knowledge of measuring air flow through ducts.








    Sent from my iPhone using Tapatalk

  2. #28
    Join Date
    Oct 2011
    Location
    Gladstone, Oregon (Portland)
    Posts
    714
    Post Likes
    ^^^ that.

  3. #29
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes
    Quote Originally Posted by Core_d View Post
    Help me understand this, you can move 1000 fpm velocity through 20ft of 12” duct at .05 static but at 100ft same size and same velocity I have .25” static?(you did mean .25 and not 2.5 correct?).

    Say if i have 100’ of 12” duct and i measure .05” static at the outlet of the duct with the grill removed am i moving 380cfm at less than 500fpm?

    Or do i need to measure the static pressure drop between inlet and outlet, total equivalent length of duct, diameter of duct and FPM to determine CFM?

    Ductulators and duct curve charts are not “friction charts” they are really FRICTION LOSS CHARTS.

    After reading your post im a bit confused as to how to use this info for practical purposes and what measurements need to be taken to determine what.

    Using TESP and a fan curve chart is easy enough and sizing a duct using a ductulator and a standard .01 friction loss is easy enough but i guess i lack the real intimate knowledge of measuring air flow through ducts.








    Sent from my iPhone using Tapatalk
    You would measure the static at the beginning of the run, and at the end. That friction loss then compared in a FR slide rule, would tell you how much air you are moving. If you can calculate the TEL of that run.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. Likes Core_d liked this post
  5. #30
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes

  6. #31
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    5,697
    Post Likes
    Quote Originally Posted by Core_d View Post
    Help me understand this, you can move 1000 fpm velocity through 20ft of 12” duct at .05 static but at 100ft same size and same velocity I have .25” static?(you did mean .25 and not 2.5 correct?).

    Say if i have 100’ of 12” duct and i measure .05” static at the outlet of the duct with the grill removed am i moving 380cfm at less than 500fpm?

    Or do i need to measure the static pressure drop between inlet and outlet, total equivalent length of duct, diameter of duct and FPM to determine CFM?

    Ductulators and duct curve charts are not “friction charts” they are really FRICTION LOSS CHARTS.

    After reading your post im a bit confused as to how to use this info for practical purposes and what measurements need to be taken to determine what.

    Using TESP and a fan curve chart is easy enough and sizing a duct using a ductulator and a standard .01 friction loss is easy enough but i guess i lack the real intimate knowledge of measuring air flow through ducts.








    Sent from my iPhone using Tapatalk

    You are correct because at the same velocity your friction rate increases with the increased length & also about my decimal being in the wrong place, it should be .25. Now I have only measured static at the beginning of a run but I would assume the static would decrease proportionally as you get further to the end of the run. I only measure velocity at the outlet of duct & I would assume there would be very little static near that point. I was never schooled in duct design & whatever I've learned & think I know just comes from my own reading & research so I'm definitely no authority on this issue.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.

  7. Likes Core_d liked this post
  8. #32
    Join Date
    May 2017
    Location
    New jersey
    Posts
    46
    Post Likes
    Thread Starter
    ok system is brand new only 2 months old. manufactures specs say constant cfm ecm fan motor will deliver 700 cfm at all times so i am pretty sure its moving 700 cfm im just not completely understand how when its only 12" duct... keep in mind there is only 14 feet of return flex and 55 feet of supply flex
    A noisy AC isnt just noisy its ALSO Inefficient

  9. #33
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes
    Quote Originally Posted by freonfreak View Post
    ok system is brand new only 2 months old. manufactures specs say constant cfm ecm fan motor will deliver 700 cfm at all times so i am pretty sure its moving 700 cfm im just not completely understand how when its only 12" duct... keep in mind there is only 14 feet of return flex and 55 feet of supply flex
    Usually they say will move set CFM at up to X amount of static/esp. Which is usually .8 or 1" of esp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #34
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    20,485
    Post Likes
    Max external static is often on the nomenclature tag these days.

    A few years ago, had this heat pump tripping out on high head. TESP was 1.0" wc, but the tag said max was to be 0.6", new York RTU. So that means too much airflow restricted, on the order of 67%. Which is approaching twice the max rating.
    If you were a real tech, you'd solder a relay on that board and call it good to go.

    I do a triple evac with nitro to remove non condensables.

  11. #35
    Join Date
    May 2017
    Location
    New jersey
    Posts
    46
    Post Likes
    Thread Starter
    i think everyone is missing my point.the duct size is to small as per the duculator and recommended .05 column you should size ducts for but with 0.43 total static clearly the ducts are not to small soo what is going on is the duculator wrong or am i loosing my mind on this one!!
    A noisy AC isnt just noisy its ALSO Inefficient

  12. #36
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes
    Quote Originally Posted by freonfreak View Post
    i think everyone is missing my point.the duct size is to small as per the duculator and recommended .05 column you should size ducts for but with 0.43 total static clearly the ducts are not to small soo what is going on is the duculator wrong or am i loosing my mind on this one!!
    Its more your understanding of duct work sizing that is wrong.

    There is NO you should use .05 friction rate. Its just a incorrect rule of thumb.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #37
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes
    Did you take your return static at the air handler between it and the filter. Where was your probe for the supply static. Does the air handler have a plenum, and then the 12" flex is connected to the plenum?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  14. #38
    Join Date
    May 2017
    Location
    New jersey
    Posts
    46
    Post Likes
    Thread Starter
    return static between air handler and filter is 1.1.. probe was at beginning of supply flex witch is just a collar tapped onto air handler..
    A noisy AC isnt just noisy its ALSO Inefficient

  15. #39
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,020
    Post Likes
    Quote Originally Posted by freonfreak View Post
    return static between air handler and filter is 1.1.. probe was at beginning of supply flex witch is just a collar tapped onto air handler..
    If return static alone is 1.1". Then you can't have a total static of only .43"
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 3 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.