    YORK YVAC 307 SCREW COMPRESSOR FAILING LOW DISCHARGE SUPERHEAT R-134A

    Hi guys new to the site here, but not new to the Hvac business, been doing it since 1977, I am a contractor in Southern California, well I got a york ycav that is really twisting my tail, got called out to site and I am told the # 2 compressor is failing on low discharge superheat, I look it over and see feed and drain valves are new and also the liquid level sensor in the flash tank, this chiller is air cooled and about 10 years old, the stepper modules are still original, so I reset it and watched for about 2 hours, r134 refrigerant, chiller set point 42 degrees, had 36 suc 130 discharge at 62 ambient, suction superheat 14.5 discharge super heat 5.4 and fighting to get up to 10 degrees, motor temps T1 68 T2 77 T3 78, 66% speed, economizer valve on,
    Drain valve 75% feed valve 45 %, now the flash tank showed 0 % and bouncing to 5 and back to 0% , oil level on sperarator is just show a little in upper sight glass, but after 15 min of operation the motor temps were in the dumpster avg 66 degrees, failed low discharge super heat around 4 degrees, I did verify the drain and feed valves in service mode are opening and closing, customer assures me that he was there when the charge was weighed in 177lbs, the level sensor and valves were installed 3 weeks ago and customer said it will stay on line for more that 10 mins, if I remember correctly 10 mins is the max time for this Chiller wit low super heat on suction or discharge, the level sensor is the PEEK sensor and you are able to calibrate it,I thought that maybe the refrigerant is oil laden, and also going calibrate the level sensor, the amp draw looked ok, need to get the reading on that, also thought economizer is pulling liquid off of flash tank if the level is high flooding the lobes, can’t dischar above 105 degrees, well got invited Back on Wednesday to do some more digging on this chiller, well sorry to be the new guy here and drop a bomb, but any feed back would be helpful thanks for taking the time to read this book-lol

  2. #2
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    1,660
    Post Likes
    Probably a bad temp sensor.
    If you dont stand behind our troops, please feel free...........to stand in front of them.

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,601
    Post Likes
    Quote Originally Posted by chillrdude View Post
    Probably a bad temp sensor.
    yup. the problem with display panels is that nearly every tech walks up and believes them. verify all values before you use them. temp and pressure are usually pretty easy to verify. your suction temperature sensor is likely to have failed. your oil separator also has too much oil in it. these chillers need very little oil and too much can also cause issues like yours.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

    Technically speaking, they are all heat pumps.

  4. #4
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    897
    Post Likes
    There is a blue letter about installing new valves on a older chiller, the connection at the valve is is where you disconnect for the cable. A new cable that goes back to the valve controller should be installed as well. If not done valve can act up, closed is open open is closed. If that were the case you can flood the evap. more then likely the valves may close thinking they were opening and shut you down on low suction. If you can see the valves respond correctly to commands thru the sight glasses good. Confirm if new cables were installed that they landed on the correct output, drain is drain feed is feed. Getting the cables pulled in is a pain.
    Pull power to the economizer valve and see if that helps. The alarm shut down is 85% full on the flash tank. If the level sensor is off you could get liquid in the compressor thru the econo. line.
    Verify all sensors, oddly enough if the level sensor is seeing 35% a lot of times the valve is 30-35% open as well. A suction line sensor that is off will get you a flooded evap. and low discharge temperature. Let know what you find.


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Jan 2019
    Location
    huntington beach calif
    Posts
    7
    Post Likes
    Thread Starter

    york ycav 307

    Quote Originally Posted by jayguy View Post
    yup. the problem with display panels is that nearly every tech walks up and believes them. verify all values before you use them. temp and pressure are usually pretty easy to verify. your suction temperature sensor is likely to have failed. your oil separator also has too much oil in it. these chillers need very little oil and too much can also cause issues like yours.
    Hi Jayguy
    well i did check the suction temperature and it was off by 12 degrees, had some sensors from a ycas, replaced it and all the numbers came back to the correct readings, 22 degree disc sh , 10 suction sh, motor temps 115 -125 degrees, i did check the cables from step controller to new valves and they are wired correctly, verified valve operation and they are opening and closing properly, will do a drive by on it tommorow to make sure it is all good, thank you for your input on this i really do appreciate it, patrick

  6. #6
    Join Date
    Aug 2013
    Posts
    6
    Post Likes
    just had the same problem the suction sensor reading high flooding the compressor driving down the discharge temperature its the same thing when the trane rtaa chillers does it.

  7. #7
    Join Date
    Jun 2008
    Location
    Ohio
    Posts
    27
    Post Likes
    The suction temp sensors on those are junk. I change them all of the time. The problem is they’ll read 5,10,15 degrees off, not 50 degrees off. Sometimes it’s not that far off so you don’t question it, you just trust the sensor. I have learned to never trust any of the sensors. 90% of low d.s. faults are caused by that. Once in a while you get a bad level sensor, and some carryover through the economize line.