  1. #14
    Join Date
    Sep 2011
    Posts
    35
    Post Likes
    Thread Starter
    We tried everything even replaced the main board and same error showed up. Ended up bypassing the board when it came to heat mode. Cooling still passes through the board and worked fine.


    Sent from my iPhone using Tapatalk

  2. #15
    Join Date
    Aug 2016
    Location
    PA USA
    Posts
    42
    Post Likes
    Check your contactor(s) coil resistance. Higher resistance will cause a voltage drop back to the board. Board will lock out on 9 flash limit code.

  3. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,177
    Post Likes
    If I may...you also want to check for your limit switches for a short to ground that shows on your DMM. This allows excess current to flow though the limit circuit, and the effect is the same as a high current contactor coil.

    I have replaced several limits that show less than OL with the wires disconnected.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #17
    Join Date
    Oct 2018
    Location
    Nc
    Posts
    37
    Post Likes
    Interesting, been in the field for few years, didn’t run cross the issue before so sorry I can’t help, still have to learn a lot from you guys.


    Sent from my iPhone using Tapatalk