    Quote Originally Posted by Snapperhead View Post
    Im still waiting for the recovery machine to suck it out .. and it's given me some time to think , and I'm thinking those rubber O-rings do play a role in Sealing because there is no Teflon rings in there and I doubt they would rely on a Brass to Brass seal ....ya think ?

    There are new Orings in the unit ..
    Soon as you remove the plastic dust covers you can see them.
    The O-Ring is the seal. A little oil MUST be applied to the O-Ring when tightening.

    Another reason to cut them out and replace!

  2. #28
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,540
    Post Likes
    I believe Hoshi's pre-charged connectors are Aeroquip Series 5780, which use the O-rings for sealing during connecting, but the final seal is metal to metal.

    Name:  Aeroquip-5700 Couplings.png
Views: 78
Size:  433.5 KB

  3. #29
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    5,108
    Post Likes
    Thread Starter
    Well aint that sumpthin

  4. #30
    Join Date
    Jan 2010
    Posts
    14,751
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Well aint that sumpthin
    Well....is it done ?

  5. #31
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    5,108
    Post Likes
    Thread Starter
    I think my pump finally quit. I ran some errands and after 6 hours its only recovered 11 lbs . Im screwed. WTH can I do now. Nothing until wed.

  6. #32
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    5,108
    Post Likes
    Thread Starter
    Finally some luck , my buddy was working across the street ! Borrowed his unit and got her emptied.

    Ok so im a big dummy. I shoved a ice pick into the metal cover and saw the piercing blades are behind it !!!!!

    SOB

    So the lineset doesnt do the piercing... It merely shoves against that metal cover and the blades poke thru .. and the blades end up going inside the lineset !

    Whoooda thunk

    Got it vacuumed , charged , and it just dropped a load of ice

    Soaped the fittings real good and no bubbles

  7. #33
    Join Date
    Jan 2010
    Posts
    14,751
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Finally some luck , my buddy was working across the street ! Borrowed his unit and got her emptied.

    Ok so im a big dummy. I shoved a ice pick into the metal cover and saw the piercing blades are behind it !!!!!

    SOB

    So the lineset doesnt do the piercing... It merely shoves against that metal cover and the blades poke thru .. and the blades end up going inside the lineset !

    Whoooda thunk

    Got it vacuumed , charged , and it just dropped a load of ice

    Soaped the fittings real good and no bubbles
    👌

  8. #34
    Join Date
    Aug 2001
    Posts
    163
    Post Likes
    I someone is determined the fittings are available from Hoshi.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.