    O-Ring ;-)

    RNG01534 is the good one !

    Thank you all !


    Envoyι de mon iPhone en utilisant Tapatalk

  2. #41
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,838
    Post Likes
    I’m a trane technician x6.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  3. #42
    Join Date
    Dec 2018
    Location
    Texas
    Posts
    8
    Post Likes
    Isolate compressor and transfer your refrigerant over to the evaporator. You can remove the plug but will likely see some oil there. Have a small can/bucket ready to catch the oil. Clean the threads and apply 567 locktite and a new oring then reinstall bolt. Vacuum compressor and open the valves. If you loose more than half a pint of oil I’d add that amount back into the system