    Determining Gas Input

    So I know how to determine gas input in a residential application. But I am in a light commercial role and would like to know how you determine gas input when you have a rather large building that you can’t just go around and cut fuel off to appliances.

  2. #2
    Join Date
    Jul 2008
    Location
    Nova-Scotia, Canada
    Posts
    456
    Post Likes
    Errr. Rating plates?

  3. #3
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Next to impossible. You can get exact airflow measurements, check delta t and plot it on manufacturer chart or use btu = cfm x deltaT x 1.08 and account for efficiency of the furnace


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,103
    Post Likes
    Clock the meter

    Sent from my SM-G920R4 using Tapatalk

  5. #5
    Join Date
    Oct 2018
    Posts
    39
    Post Likes
    Thread Starter
    Quote Originally Posted by Spitz View Post
    Clock the meter

    Sent from my SM-G920R4 using Tapatalk
    I understand that, but how do you clock a meter at a place that can’t have all of the gas equipment shut down? Is there a meter of sorts that can be put in line to the equipment

  6. #6
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,103
    Post Likes
    Could buy one on ebay for $100

    Sent from my SM-G920R4 using Tapatalk

  7. #7
    Join Date
    Oct 2018
    Posts
    39
    Post Likes
    Thread Starter
    Quote Originally Posted by Spitz View Post
    Could buy one on ebay for $100

    Sent from my SM-G920R4 using Tapatalk
    What kind of meter is it

  8. #8
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,103
    Post Likes
    One like on the side of a house

    Sent from my SM-G920R4 using Tapatalk

  9. #9
    Join Date
    Aug 2002
    Location
    Cincinnati, Ohio
    Posts
    3,048
    Post Likes
    How do you determine the btus on commercial equipment when you can't clock the meter? What about LP?
    captain CO

  10. #10
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes
    Quote Originally Posted by Jim Davis View Post
    How do you determine the btus on commercial equipment when you can't clock the meter? What about LP?
    Analyzer. 6-9% or 3-6% depending on burner

    Btu = cfm x deltaT x 1.08

    Or

    Btu = gpm x deltaT x 500

    Can i get my recertification card now?


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Oct 2018
    Posts
    39
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    Analyzer. 6-9% or 3-6% depending on burner

    Btu = cfm x deltaT x 1.08

    Or

    Btu = gpm x deltaT x 500

    Can i get my recertification card now?


    Sent from my iPhone using Tapatalk
    Wouldn’t you need to know BTU to determine CFM? And to get GPM would you not need to clock a meter? Or would total static be good enough for the situation

  12. #12
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,906
    Post Likes

    Determining Gas Input

    For CFM use a flow hood, traverse the duct with pitot tube, or hot wire anemometer, or take TESP and use the manufacturer blower curve chart to plot CFM.

    For GPM, take deltaP across pump, boiler, unit and convert to ft/head. Use a pump curve chart or manufacturer chart to plot GPM using head.

    Then fill in the formula


    Sent from my iPhone using Tapatalk

  13. #13
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    11,841
    Post Likes
    Quote Originally Posted by dustinwest View Post
    Or would total static be good enough for the situation
    Static pressure or duct traverse will work.

    As long as you get an accurate CFM reading the formula will tell you if your BTUH output is within the rated output of the unit.

    Output is the only important number anyway.

    If output isn’t correct, adjust manifold pressure or change the orifices as necessary.

    Be sure you are using a combustion analyzer when making any adjustments.