    Honeywell W7100J with 10 second delay

    I have a Honeywell W7100J heating controller with only a 10 to 15 second delay between stages. There is no plug in the bottom. It is set at 140 degrees, 1:1 ratio, 16 throttling range (max). Any ideas?

  2. #2
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,108
    Post Likes
    Just pulled up the W7100J manual, it's supposed to be 2 minutes between stages, if you look at the troubleshooting in the back with the test plug in the stages will stage up every 10 seconds.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  3. #3
    Join Date
    Jul 2002
    Posts
    1,278
    Post Likes
    Thread Starter
    Plug not in. Must be internal. Thanks

  4. #4
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,108
    Post Likes
    Does it have the hole for a plug with the red insert in it?
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned