    frost may or may not appear on the suction line, it depends on box temperature, system design, and charge ... do not use a frost line to charge a cap tube unit

    charge for ' around 10 degree superheat ' ( evaporator outlet ) when your box temperature starts to hit around 42 - 44 degrees, make sure you maintain ' around 10 degrees superheat ' ( evaporator outlet ) a few degrees lower that your off temperature setting ( do not allow system to flood, IE overcharged )

    cap tube systems are charged by targeting the lowest suction pressure / temperature while still maintaining superheat, also, pay attention to your ambient conditions

    or weigh in your charge