Page 2 of 2 FirstFirst 12
Results 14 to 17 of 17
  1. #14
    Join Date
    Aug 2004
    Location
    Raynham, MA
    Posts
    125
    Post Likes
    Thread Starter
    Thank you everybody. Happy Holidays!

  2. #15
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,212
    Post Likes
    My money says switch stuck closed. Replace the motor.

    The board has to see the switch circuit open at first, and THEN close when the motor spins up.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  3. #16
    Join Date
    Dec 2018
    Posts
    1
    Post Likes
    3 blinks... open pressure switch......

  4. #17
    Join Date
    Aug 2004
    Location
    Raynham, MA
    Posts
    125
    Post Likes
    Thread Starter
    Ill never find out; I was hired to troubleshoot, I guess. The facilities personell will change out the whole motor with the end switch.
    I.m.o. the end switch was stuck closed cuz when I pulled apart the orange wire then plugged it back in, the inducer fan started up and the try cycled through the heat. But then would not cycle on again after satisfying temp unless I did the orange wire thing... Sticking closed.

    And yes. I was on part being a wimp in the 22 degrees and hoping to initially score a quick support of my theory whilst warming up. My tools were out of sorts and those nuts on the end switch are a pain in the ... to remove with needle nose.
    Thx everyone.