    May 2017
    New jersey
    90% furnace alot of Sediment in condensate trap
    Hey guys I have a 90% furnace that is only one and a half years old today I got called out and found a condensate trap inside the furnace filled with sediment also the collector box outlet to the trap was plugged shot I checked the gas pressure that is fine but I noticed the flu pipe is 38 feet over it’s maximum allowed distance I have seen furnaces go out on high limit and even roll out when the flu pipe is either too small or too long of a run just wondering if anyone else has ran into a situation like this I am pretty sure the build up in the secondary heat exchanger is do too the flu pipe being too small and too long
    Make and model?
    Realize that this could be normal as this is from the outside air being drawn through the hx and then mixed with the condensation.
    Also, some furnace heat exchangers start to fail and this is the first place you will find the "debris" from it.
    Sep 2014
    NW Arkansas
    Could it be from something making a nest in the exhaust such as a wasp nest? Does the exhaust slope to or away from the unit?
    Sent from my SM-G892A using Tapatalk
    May 2017
    New jersey
    Rheem r9270k btu flu slopes toward furnace but flu size is deffinetly to small