    Walk in freezer R448A



    Received a call on this walk in freezer another company installed. System is remoted 2 floors above box. R448 refrigerant with -10 setpoint for Freezer. Looks like this unit has an MOP txv valve at 35 psig. Has a headmaster valve for 225 psig. Unit is actually at temp but looks as if in the colder mornings and nights it may be low on charge causing this iceing issue. I will have more info tomorrow. Just wanted some initial thoughts.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    R-448A is a replacement for R-404A

    Treat it as the same.

    Is it low on charge? Clear the glass. 225# headmaster is fine!
    Are you aware how a headmaster works?

    That ice tells me its coming out of defrost a little early possibly a bad heater.

  3. Likes WT70 liked this post.
  4. #3
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Yes I’m familiar with headmasters, but looking at the ice formation around the txv and inlet of coil seems excessive like it was low on refrigerant enough to where the headmaster couldn’t keep pressure up. I will know more tomorrow when I have another guy so I don’t have to go back and forth 2 stories since the location is a pain.


    Sent from my iPhone using Tapatalk

  5. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    Quote Originally Posted by Bworth74 View Post
    Yes I’m familiar with headmasters, but looking at the ice formation around the txv and inlet of coil seems excessive like it was low on refrigerant enough to where the headmaster couldn’t keep pressure up. I will know more tomorrow when I have another guy so I don’t have to go back and forth 2 stories since the location is a pain.


    Sent from my iPhone using Tapatalk
    Could be low
    Valve out of adjustment
    Garbage in the strainer (Hope not being hard soldered..Bring an extra valve just in case)
    Not properly charged for the headmaster .......now its cool at night.

  6. #5
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Could be low
    Valve out of adjustment
    Garbage in the strainer (Hope not being hard soldered..Bring an extra valve just in case)
    Not properly charged for the headmaster .......now its cool at night.
    Yes it was installed in August in Texas so this is its first winter. It’s been getting high 20’s low 30’s overnight for a week or so now.


    Sent from my iPhone using Tapatalk

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    Now the question is.........(If its low)

    Is there a leak or just not charged properly to begin with?

  8. #7
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Now the question is.........(If its low)

    Is there a leak or just not charged properly to begin with?
    Lol, I was just thinking that. Guess a leak check is in place.


    Sent from my iPhone using Tapatalk

  9. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    I would get there early in the morning............
    If it only takes maybe a lb with a micro channel your probably good.

    If its actually short well have fun!

  10. Likes Bworth74 liked this post.
  11. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    Post pics of the condensing unit

  12. #10
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Post pics of the condensing unit
    Ok I will do that tomorrow


    Sent from my iPhone using Tapatalk

  13. #11
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    621
    Post Likes
    Correct me but I charged a big walking in summer with headmaster. Cleared the glass but didn't add an extra amount for winter. Giant box filled w/ bannanas. Added and working nice but no ice just not cooling.

  14. #12
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    You have to add the additional charge for the head pressure control valve to be able to flood the condenser.
    Oh, and you should start a new thread.

  15. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    You don't think that's steam freezing?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. #14
    Join Date
    Jun 2007
    Location
    SoCal
    Posts
    139
    Post Likes
    Quote Originally Posted by Bworth74 View Post


    Received a call on this walk in freezer another company installed. System is remoted 2 floors above box. R448 refrigerant with -10 setpoint for Freezer. Looks like this unit has an MOP txv valve at 35 psig. Has a headmaster valve for 225 psig. Unit is actually at temp but looks as if in the colder mornings and nights it may be low on charge causing this iceing issue. I will have more info tomorrow. Just wanted some initial thoughts.
    how is this defrosting ? hot gas or electric ?? how many times a day and what is the duration ?? is there any termination ? are the fans shutting off in defrost ?? more information is needed

  17. #15
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Sorry still scheduling with customer to get in and make a good diagnosis. I will post as soon as I have the information.

  18. #16
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    So did you calculate the winter charge per Sporlans bulletin ?

  19. #17
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    So did you calculate the winter charge per Sporlans bulletin ?
    I did not. Still evacuating where can I find that info please.


    Sent from my iPhone using Tapatalk

  20. #18
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    R404a is a great refrigerant and probably half the price of R448a. A third the glide as well.

  21. #19
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    107
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    R404a is a great refrigerant and probably half the price of R448a.
    Almost half price at United Refrigeration. R448A is definitely more expensive for sure!


    Sent from my iPhone using Tapatalk

  22. #20
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Something interesting to note that I see when people start working with a new refrigerant.

    They seem to forget basic refrigeration diagnostic methods

    Charge, Superheat, operating pressures, defrost lengths and proper termination, etc.

    I have done a lot of work with R448a both Racks and Self contained/conventional. It runs almost the same as R22, but lower discharge temps.

    Go through from start to finish and make sure it's all operating correctly, I bet you will find the problem along the way. It's just a freezer.




    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •