    Walk in freezer R448A



    Received a call on this walk in freezer another company installed. System is remoted 2 floors above box. R448 refrigerant with -10 setpoint for Freezer. Looks like this unit has an MOP txv valve at 35 psig. Has a headmaster valve for 225 psig. Unit is actually at temp but looks as if in the colder mornings and nights it may be low on charge causing this iceing issue. I will have more info tomorrow. Just wanted some initial thoughts.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,061
    Post Likes
    R-448A is a replacement for R-404A

    Treat it as the same.

    Is it low on charge? Clear the glass. 225# headmaster is fine!
    Are you aware how a headmaster works?

    That ice tells me its coming out of defrost a little early possibly a bad heater.

  3. Likes CRussell1975 liked this post
  4. #3
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    103
    Post Likes
    Thread Starter
    Yes Iím familiar with headmasters, but looking at the ice formation around the txv and inlet of coil seems excessive like it was low on refrigerant enough to where the headmaster couldnít keep pressure up. I will know more tomorrow when I have another guy so I donít have to go back and forth 2 stories since the location is a pain.


    Sent from my iPhone using Tapatalk

  5. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,061
    Post Likes
    Quote Originally Posted by Bworth74 View Post
    Yes I’m familiar with headmasters, but looking at the ice formation around the txv and inlet of coil seems excessive like it was low on refrigerant enough to where the headmaster couldn’t keep pressure up. I will know more tomorrow when I have another guy so I don’t have to go back and forth 2 stories since the location is a pain.


    Sent from my iPhone using Tapatalk
    Could be low
    Valve out of adjustment
    Garbage in the strainer (Hope not being hard soldered..Bring an extra valve just in case)
    Not properly charged for the headmaster .......now its cool at night.

  6. #5
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    103
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Could be low
    Valve out of adjustment
    Garbage in the strainer (Hope not being hard soldered..Bring an extra valve just in case)
    Not properly charged for the headmaster .......now its cool at night.
    Yes it was installed in August in Texas so this is its first winter. Itís been getting high 20ís low 30ís overnight for a week or so now.


    Sent from my iPhone using Tapatalk

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,061
    Post Likes
    Now the question is.........(If its low)

    Is there a leak or just not charged properly to begin with?

  8. #7
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    103
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Now the question is.........(If its low)

    Is there a leak or just not charged properly to begin with?
    Lol, I was just thinking that. Guess a leak check is in place.


    Sent from my iPhone using Tapatalk

  9. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,061
    Post Likes
    I would get there early in the morning............
    If it only takes maybe a lb with a micro channel your probably good.

    If its actually short well have fun!

  10. Likes Bworth74 liked this post
  11. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    19,061
    Post Likes
    Post pics of the condensing unit

  12. #10
    Join Date
    Aug 2018
    Location
    Fort Worth, Tx.
    Posts
    103
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Post pics of the condensing unit
    Ok I will do that tomorrow


    Sent from my iPhone using Tapatalk

  13. #11
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    408
    Post Likes
    Correct me but I charged a big walking in summer with headmaster. Cleared the glass but didn't add an extra amount for winter. Giant box filled w/ bannanas. Added and working nice but no ice just not cooling.

  14. #12
    Join Date
    Jan 2010
    Posts
    15,201
    Post Likes
    You have to add the additional charge for the head pressure control valve to be able to flood the condenser.
    Oh, and you should start a new thread.

  15. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,969
    Post Likes
    You don't think that's steam freezing?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

Page 1 of 5 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.