    1.5 ton A/C with a 90' riser. Hope that suction line is only 1/2"(A velocity of roughly 1440FPM). Other wise virtually have no oil return.

    Guessing you did use a trap at the bottom of the riser, and an inverted trap at the top of the riser on all of the long line sets?