Results 14 to 23 of 23
    Southold, NY
    Ive found with Traulsen freezers insert the sensor with the wires facing down. Keeps moisture from getting in and freezing.
    I do that with all sensors now!
    Jan 2010
    Why didn't you tell me that last week !
    So I'll be going back within a year ? I did a monkey see, monkey do.
    Southold, NY
    You Screwed Up..........................
    You Trusted Me!
    Jan 2010
    I should've done a screwed down it sounds like!
    Mar 2015
    Medford, N.Y.
    Hey OP, I would be interested in the Mfrg name. I like to see stuff on my own..
    Depending,what is the Mfrg limit for the highest ambient temp for running their units in the heating mode??
    Nova-Scotia, Canada
    York thermistors for the last while have been utter garbage. I wasn’t too happy when I had to patch crushed and split condenser tubes on an rtu that had already had the coil sensors replaced. Unit goes into defrost, says holy coil is hot, go back into heat mode. Then the coil freezes and the ice crushes the tubes.
    To top it off those sensors aren’t exactly free... neither is the bill to the customer for fixing a coil and charging a dozen pounds of juice...
    Southold, NY
    So....
    Any Update?
    Jul 2009
    Columbia, MD
    Definitely line size problems.
    I would have trapped the lines even if the mfg said no.
    System 1 seemed oil logged in cooling mode. Thats why the SH was low.
    Heres what i would do.
    Install an icm333 with icm380(pressure transducer). Change the CFM to a ball bearing type.
    Set the icm333 to maintain 365psi
    Run the system in cooling mode. With the icm333 cycling, I would add gas until my discharge line temp was around 165*. And see what the compressor sh looks like.
    Monitor operation with icm cycling.
    Take the icm out of play and monitor operation and see what the discharge line temp and compressor sh does.
    Numbers id like to see at all times in ac mode
    140-165* discharge line temp
    Compressor sh range from 18-25*
    Compressor suction temp no more than 65*
    Verify txv and eev functional and no strainers clogged.
    Apr 2003
    St. Louis
    Every condenser has a total !ine lenght requirement. The compressor doesnt care are how long the line lenght is But the size of what the compressor capacity is does. When you add oil to a long line system the compressor body can only hold so much oil, at some part of the run cycle all the oil will come back to the COMPRESSOR, have to much bye bye compressor.
    Jul 2009
    Columbia, MD
    You must also add extra oil for added length. Manufacturers might not say so but, you really need to. Liebert is good about telling you how much oil.
    If what i said above doesnt help, i would strongly consider adding a oil seperator in the condenser. Very easy to do, just cost money.