Old house with high humidity
I have a 1950's home on the water in Florida. Earlier this year, I had a VS HVAC installed. When it's warm outside, my HVAC dehumidifies just fine. However, during the times when there's no need for cooling, my humidity goes through the roof. 70+%. I've been using an older standalone dehu which will pull out about 5 gal / day when the humidity is high. It stops pulling much of anything in the mid 60%'s though. And when we're away from home, we have to unplug the unit, as there's no one to empty it.
I'm looking to have a whole house unit installed. It seems Ultra Aire's 120V would fit into our HVAC closet, and I'm not sure if our contractor could make a traditional horizontal unit work in the space without some major "surgery."
My house is 3200 sq ft, 1950's, with a crawl space (no vapor barrier), and in an area with a high water table. The home is occupied by four people. Would the 120V work for our home? Or do I need to look at a larger unit?
High RH goes to low RH. A blower door test will tell you how tight the house is. Have you sealed all pipe and wire penetrations in the crawl space, windows ,doors and attic. If you do some research on dehumidifiers you will find stand alone models are rated at 95% RH and 80*. Whole house are certified at 60%. Contact your electric company they might offer a energy audit that includes blower door test mine came out for $50.
Sorry about missing your post and my slow response.
With sand/high water table, a vapor barrier on the earth and blocking the outside air vents in the crawlspace will reduce moisture in the home.
A Ultra-Aire 120V is a good choice, very high efficiency and a good fan with merv 13 air filter. Important to get connection of the dry air from the dehu to the a/c supply with a return from the open part of the home to the dehumidifier. If you seal the crawlspace and cover the earth, include a small supply to the crawlspace from the dehumidifier. Where in FL is this?
Let us know how it all works out.
Regards Teddy Bear
IMO...
The first thing I would do... is stop the moisture from coming into the crawl space!
Then re-evaluate the size of de-hum you need.
What TB says above is good information!
GA-HVAC-Tech
I agree with ga hvac tech. Seal your crawl space!!!
My next question is when you say variable speed are you talking about the blower or do you have a high end trane xv20 or a lennox xc25 variable speed compressor. Because those you can set up to dehumidify your home with no need for a stand alone dehumidifier.
If you are dead set on getting a stand alone dehumidifier look into the Lennox healthy climate hcwh070 hcwh090 hcwh120
You can tie those into your existing ductwork and have them set up to come on when your main unit shuts up. You can control it with an external controller or have it controlled with the onboard controller. Pipe it into the exsisting drain or put it on a condensate pump.
First, thank you all for the replies. I'm in the Jacksonville, FL area. In our last home, which was a 1920's home but on drier soil, we had the crawlspace sealed (Clean Space). That worked really well. For this house, we are planning on undertaking a major renovation, and so I didn't want to go through the expense when it would likely be damaged or destroyed once we start renovation.
As for my current HVAC system, it's a Bryant Evolution (same as Carrier Infinity). It can dehumidify beyond the set temperature, but only to a point. All summer, the indoor humidity was great, although we may have had to cool a bit beyond what we would have normally wanted.
The real issue is these months where not cooling or heating. The humidity outside stays well about 70%, which means the indoor humidity is at least that.
Overall, it sounds like a mistake to invest more in dehumidification until I do something about the crawlspace though. Would installing a 6mil visqueen over the earth and sealing the crawlspace vents help significantly? Or look into actually having the crawlspace more professionally sealed as I did in our previous house?
I'm not opposed to investing what's needed to do things right - I'm just after more comfortable home.
Have it professionally sealed and then go from there.
I would have a pressure test done on your ductwork as well. Especially if its over 30 years old.
Taking the help of the professional contractor can help you in getting the best solution for it.
If you are going to do a remodel extensive enough to potentially damage the crawl space plastic... then yeah... maybe a professional crawl space job is not the best thing to spend $$$ on short term.
Portable de-hums come with a 'pump'... they cost a little more, yet automatically empty themselves... usually last 2-3, maybe 4 years before failing. I use one in my garage to keep the metal working machine shop from rusting.
Suggest to get 2x portables... better to 'over-capacity; your de-hum needs, and let them run 24/7. They will cycle off when they reach your set point.
That will keep you comfortable and resolve the potential damage from high moisture levels.... short term. Note this is not a long term solution... rather a short term solution to 'get by' until you do the remodel.
If it were me... when I budgeted for the remodel: I would add in to have the crawl thoroughly sealed by a professional company... they use higher quality products that last a lot longer than a roll of plastic from HD...
Humidity can subtly cause a lot of damage... as well as grow organic stuff that is not healthy. And letting ones house get full of that organic stuff... well it costs a small fortune to fix that... not to mention the health hazards...
IMO better to keep that humidity under control!!!
GA-HVAC-Tech
The crawl space should be sealed before installing the dehumidifier. Humidity will surely going to damage your furniture and appliances and promote mold and rust. It is going to cause a lot of health problem too. So better get it done.
VS a/c is slightly better that conventional a/c or heat pumps. But the most sophisticated VS a/c are unable to maintain <50%RH with a +40% sensible cooling load. During rain and evenings a small whole house dehumidifier like the Ultra-Aire dehumidifier is needed. Allowing a home to be +60%RH for an extended time grows mold whereever the high humidity is.
10 mil plastic covering all of the earth and closing the crawlspace vents is important. but keep the upper house dry ASAP. You could park a Ultra-Aire 70 in the home with a house to a drain now. Move it to the crawlspace when crawlspace ready.
Timing is important.
Keep us posted.
Regards Teddy Bear