    Walk in cooler temperature not lowering

    Hello all, I am an equipment owner and in no way knowledgable about refrigeration. I have a vollrath roof top compressor controlled walk in cooler . Two weeks ago the compressor died and was replaced. For a few days the temperature was holding at about 34-36 . I come in about a week later to find it at 39 degrees. Lowering the thermostat had no effect. I contact my HVAC guy who replaced the compressor and he said this was nothing to worry about.Well, I NEED the temp to be in the 34-36 range. Slowly over a few days the temp began to rise. 39 to 40, and today 41 degrees. I again contacted him but he has not yet gotten back to me. I'm a nervous wreck because the compressor repair was very costly and I fear anther costly repair. My questions are 1. This is not normal, right? 2.Without any technical info is it possible to suggest possible culprits? 3.Is there a way to keep product colder while waiting for repair man, like ice in a large chest? Thank you very much for any expertise you can impart.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,336
    Post Likes
    Was the cause of the compressor failure determined and corrected?

    Not responding is not a good sign.

  3. #3
    Join Date
    Dec 2018
    Posts
    4
    Post Likes
    Thread Starter
    The compressor was replaced with a new one.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,336
    Post Likes
    Quote Originally Posted by debbiedoescakes View Post
    The compressor was replaced with a new one.
    Compressors don’t just die. Generally there murdered. The tech should find the cause and correct that.

    As far as your current problem yes it should operate between 35 & 40*F

  5. #5
    Join Date
    Dec 2018
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Compressors don’t just die. Generally there murdered. The tech should find the cause and correct that.

    As far as your current problem yes it should operate between 35 & 40*F
    Haha! I feel like somebody murdered me! It was a very, very old compressor . Hopefully he can schedule a service call for me very soon. Any advice about the best thing to do in the meantime? I read dry ice, but I know that comes with it's own dangers.Thanks for your time, I appreciate it.

  6. #6
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    1,574
    Post Likes
    Assume you are a commercial customer for this HVAC guy. I'd start bugging him incessantly to come and Fix your cooler. That is what we do. How we keep customers.... happy.

    Also assume that you did not piss him off by not paying?

  7. #7
    Join Date
    Dec 2018
    Posts
    4
    Post Likes
    Thread Starter
    haha, no I paid him :-)

  8. #8
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    2,002
    Post Likes
    Dry ice temporarily.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,336
    Post Likes
    Our customers check each box every morning.
    If its above 40° we tell them to call.
    Walk Ins take priority over other service calls.

  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,336
    Post Likes

  11. #11
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,324
    Post Likes
    Check for icing of the evaporator coils. 34 degrees is too cold unless you have defrost capabilities.
    If it is frosted over, try turning off compressor until you can see clear through the evap coil. (Box temperature will probably rise) Turn it back on and see if you hit 34 degrees.
    If it works now, try turning stat up 4 degrees and stepping it down over a few days. A one degree setting change is going to make a huge difference if defrosting is the issue. Health code says 38 degrees is what they want. It use to be 40 and this has caused al ot of defrosting issues when requirements changed to 38.

    If coil starts freezing at one end, probably a refrigerant leak.

  12. #12
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    891
    Post Likes
    Each municipality usually has its own rules about maximum refrigerated product temps. It was 41F in my area but was recently lowered to 40F. This is the FDA max and seems to be what most health departments use.

    I have a ton of coolers with no forced defrost provisions running at 33F that do just fine, and I have a bunch more that can barely hold 40F without freezing up. There are a slew of variables that are different for every equipment setup, usage pattern, and climate. If your HVAC guy isn't well trained in refrigeration, you should seriously consider finding a refrigeration professional. It is different from HVAC.

    Sent from my Pixel 2 using Tapatalk